Please can you help me in finding the parameters needed to set overcurrent relays for a transmission line with sources from both ends?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Overcurrent Relay Settings

09/02/2009 11:49 AM

Can you please clarify? There are several types of transmission lines. And, "sources from both ends" is very confusing. Two sources and no load?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Overcurrent Relay Settings

09/02/2009 11:46 PM

Please refer to a qualified electrician or a consultants for these protection relay setting. There is few parameters need to be tested and to set it, as according to your protection level, faults level and the tripping time.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Overcurrent Relay Settings

09/03/2009 10:39 PM

In addition to other settings, one important thing you need is to enable and set up (dead bus/dead line, dead bus/live line, live bus/live line, live bus/dead line) the synch check functionality of the relay. This ensures the synchronization conditions are met before closing of the breaker. This is very important because the transmission line is fed from both ends.

- MS

__________________