Our plant always encounted power failure due to external caused,and some of our AC 3phase drive motor (415V 3phase 50Hz)equipment therefore during power failure and some raw material was stuck in the pipe line. i need to run the motor about 10min after main power failure.

Now i have 3kw motor (5.6 Ampere) ,pls advise me how to do the sizing of UPS ?

Thank you and Best Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#1

Re: UPS Sizing

09/04/2009 1:35 AM

How Many Motors??

What are Max Amps??

What Power Factor??

These will give you the size and specs for the UPS.

Contact a reputable UPS Supplier for assistance or better still contact 3-4 and ask them for recommendations.

The 10min Battery life will depend on the number & size of the battery blocks, which will be best identified by the UPS supplier.

Make sure you specify "10 minute Autonomy at end of battery life" with a discharge on 80% or less.

This is important if you need 10 minutes to clear the pipes as battery autonomy reduces with age.

A Rotary UPS will not help you since you have a 10 minute runtime requirement.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#2
In reply to #1

Re: UPS Sizing

09/04/2009 3:56 AM

Hi Sapper,

Thank you very much of your very valued infomation.

Regards

Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#9
In reply to #1

Re: UPS Sizing

09/07/2009 7:50 PM

Hi Sapper,

I have only one unit of 3Kw 3phase motor, max ampere 5.5Ampere and PF at 0.7

Thank yo very much of your prompt reply

Regards

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#10
In reply to #9

Re: UPS Sizing

09/07/2009 8:07 PM

I would suggest at least a 5-5.5kVA UPS and batteries for 10mins at EOL.

Allows for power factor and a bit load increase as the motor ages.

I would be looking at the following Suppliers: -

  • THYCON
  • Chloride

as they do UPSs for industry rather than Just IT environments.
Please Note: These are just suppliers I have worked with in my area. There may be other alternatives closer to your location

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Participant

Join Date: Aug 2009
Posts: 1
#3

Re: UPS Sizing

09/05/2009 12:11 AM

The best UPS manufactures are MGE; SOCOMEC; GE and Emerson. You can ask for the Industrial application UPS with statice bypass.

Best Regards,

MVK

Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#11
In reply to #3

Re: UPS Sizing

09/09/2009 4:47 PM

Dear MVK,

I would disagree with you Chloride is a leader in the ups industry in Europe and has a world wide service organization. They build ups up to 750kva and up to 8 can be parallel to power a 6MVA site. Their software can link multiple ups together from different facilities world wide.

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#13
In reply to #3

Re: UPS Sizing

09/09/2009 5:20 PM

MVK,

I agree with your comment for Industrial IT applications, but for Industrial Plant applications I would select Thycon, Chloride or GE over all of the rest you have mentioned, although I would argue "Best", but they are good in thier own rights.

Thycon, Chloride and GE all provide Hardened UPSs to support places like Oil Rig, Mines etc, I have not heard any comments (good or bad) about the others in these applications which is a good indicator that they are not the predominant UPSs used in this type of application.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#4

Re: UPS Sizing

09/05/2009 5:45 AM

Hello aikhh,

I am not sure how many motors you can drive from an UPS. However I list a site below which can give details of the UPS you mentioned. See below.

http://www.google.co.uk/search?hl=en&client=firefox-a&rls=org.mozilla:en-GB:official&hs=iWX&ei=IDKiSoKfJYmh4gb_saDvCQ&sa=X&oi=spell&resnum=0&ct=result&cd=1&q=UPS+sizing+for+415V+3+phase+50Hz&spell=1

Keep in touch and let me know how you get on, OK?

Take care and good luck.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Active Contributor

Join Date: Aug 2009
Location: India
Posts: 12
#5

Re: UPS Sizing

09/05/2009 1:38 PM

Hi, all of our collegues gave good ideas. definitley they are right.

I suggest a simple calculation to understand how to perform the sizing of UPS.

1. Identify the load requirement: For example 3 KW (only one motor)

2. PF at which it operates to get KVA: (taking PF 0.8) 3.75 KVA.

3. Take 10% excess : 4.125 KVA Round figure to 5 KVA. (3 phase UPS)

4. Please be aware with this UPS you cannot restart the motor but it maintains the running load.

5. Now coming to the battery bank. As you require hold up time of 10 min; specify the same to UPS vendor.

__________________
Mind is like a parachute, no use if you do not open it
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#7
In reply to #5

Re: UPS Sizing

09/05/2009 4:44 PM

Hello imandi007,

GA to you Sir.

I worked this out for all the integral electric of my computer. It needs a much smaller UPS of course I got a 12 watt just to be on the safe side. I get 15 minutes. For the cost of an UPS to power more than one motor, it would be cheaper to get a Generator? A Generator is much more versatile as well.

Take care.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#14
In reply to #5

Re: UPS Sizing

09/10/2009 7:40 PM

Hi imandi007,

Thank you very much of your info

Regards

Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#6

Re: UPS Sizing

09/05/2009 4:36 PM

all the comments so far are on target but you may also want to consider a back-up generator. The question is whether your production line can wait for the few seconds for the generator to start and come on line.

If that time will not allow for a preheat then choose a gen that starts direct. This should give you power in less than 20 seconds, and then for as long as there is fuel in the tank.

It is also possible to have a combination of both systems. the UPS for low power control circuits and the gen for the motor devices.

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#8
In reply to #6

Re: UPS Sizing

09/05/2009 4:48 PM

Hello capblanc,

I answered direct from my notification from the post which had one GA. I did not realise you had suggested a generator also, sorry.

Take care

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#12

Re: UPS Sizing

09/09/2009 4:51 PM

Hi Aikhh,

In addition to what Sapper has said when you are refering to max amps - that should be the lock rotor amps or inrush current that occurs at start up. The ups overload capaiblities must be able to handle the start up current or the ups will switch to the bypass mode or shut down.

Register to Reply
Register to Reply 14 comments

"Almost" Good Answers: