Hi all, This is Usman !
I am nowadays working at the construction site of ammonia plant (for fertilizer production), we are at the pre-commissioning stage and we haven't decided on a reliable standard procedure for the Leak Test for the Instrument Impulse Tubes.
Can anyone kindly refer me to a standard procedure which we can use at our site for LEAK TESTING OF INSTRUMENT IMPULSE TUBING. Our subcontractor is CNCEC (Chinese National Chemical Engineering Company) and their presented procedure is not impressive and has a lot of language barriers in it.
Thanks in advance
Re: Leak test for Impulse Tubing
09/04/2009 6:51 AM
What is in the tubes, at what pressure and temperature, when the plant is supposed to be running?
What is the size of the tubes?
What are the tubes made of?
What are their maximum ratings as supplied as regards pressure and temperature?
09/04/2009 12:20 PM
Lets consider the case of instrument air tubing for control valves,
The tubing is 316LSS and size is 12mmODx1.0WT and it is a Seamless stainless tube.
Any standard procedure for their leakage test ???
09/05/2009 10:41 AM
I/A is not impulse tubing.
09/05/2009 10:42 AM
They still require leak test??? I've never encountered this, usually only on impulse line for transmitters.
09/06/2009 7:56 AM
For control valves, instrument air tubing is leak tested as standard. The air headers & branches for instrument air are all tested as well the instrument air tubing from the branch to the valve.
The function of impulse tube and instrument air tubing are different but they are nevertheless tubings which require fitting and leakage test as well.
09/11/2009 11:54 AM
Please describe a procedure for the benefit of the orignal poster, as well as the rest of the forum.
Re: Leak Test for Impulse Tubing
11/07/2009 9:18 AM
Better way to check the leakage in instrument air tubing of a C/V (which you call impulse tubing) with soap solution.
Pass air thru the line, apply soap solution over the joints & observe the leakage.
03/11/2024 12:25 PM
That might work below 250Bar-litres, though it would be a very hazardous procedure above that. If passing above this point please ensure that all other CR4 readers are standing decent distance away before carrying out the test.