Hi All Electrical Engineer,
I have problem in our Sag Mill Motor which tripping on Earth Fault and block tripped on the Multilin protection relay.
This Sag Mill is driven by the 4MW / 6.6kV wound rotor, with soft stater called LRS - Liquid Resistance Stater. We don't have problem of starting since it was commision six month ago, just last week it was start tripping on above faults. Grounfd Fault tripped
Check has done.
1. Disconnect all 6 single core HV cable and megger or insulation test at 10kV megger test and the results are fairly good which are all 43 to 44 Mega Ohms.
2. Disconnect all motor lead and megger all phases are 15 Mega Ohms.
I cannot pinpoint which one is causing the earth fault tripped. It might be Multilin protection relay is faulty? or what ever thought.
Please send me your comments.
Kindly regards,
Alex