Dear All,
This is the first time i have posted in this forum after reading some comments posted by some experience engineers.
I have this problem recently, the genset is rated at 625KVA. The engine is from Korea P22LE made by Doosan, and the alternator is made by China licenced Siemens- 1FC2 355-4LB43 (4pole alternator, 400V, 50Hz, 625KVA) . During the factory testing the genset cannot be loaded beyond 30% load and no hunting experience. The load bank used is a resistive one. Technicans decided to change the speed controller and the injector pipes. but cannot improve the situation. Latter decided to change to a new AVR suspecting its the AVR faulty. The AVR used is from Taiwan Kutai EA 63-7D. However, no improvements seen, thus a new alternator is brought in from another state and couple with the Engine. This time the genset can load up to 90% load and no further because the Engine is hunting and giving white smoke then shuts down. After changing to a new injector pipe, genset can hit 95%load but similar problems experience again. Technicians check the excitor stator voltage and resistance at no load and at load, everything seems fine. Change to a US made AVR Basler AVC 63-7F but no improvements to load situation. It seems like its an engine problem but Engine maker insist its an alternator problem because of its poor efficiency. I am hoping the Engineers here can provide me with some advice. Thank you.