Maintaining Power Factor

09/14/2009 4:16 AM

I have 12MW gas engine based power plant its running parallel with grid. my problem is When cpp run in island mode(without geb) that time geb transformer power factor is 0.2 lagging. When cpp run with parallel that time power factor is 0.94 lagging So how can i maintain power factor ofgeb transformer in island mode 0.9 lagging?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Maintaining Power Factor

09/14/2009 9:15 AM

What is GEB or geb?

It may all depend on the load on the transformer (EB = Electricity board?)

How is the load sharing when it is on island mode ?

Assume you have a total Load of L with power factor say 0.85.

In island mode a load of L1 is taken by your CPP and may be the most of the load.

In this condition the geb (whatever it may be) must be taking a load L2<<L1.

This load L2 might be by itself highly lagging (which was being eventually compensated by your CPP through excitation control) or may be so low that the transformer's no-load magnetizing current is overriding all others.

If it is second part (ie the GEB transformer is on no load) then i don't think it is worth to try to compensate it.

However if it is still on sufficient load, or otherwise too, do not strain your CPP, try to find out the load power factor(s) and compensate, preferably nearer the load rather than at the transformer/ generator end.

It is purely a guess based on incomplete information

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Maintaining Power Factor

09/14/2009 3:30 PM

Put simply in parallel grid operation the rest of the power plants and power factor correction devices on the grid help correct the power factor of the entire network including your small area. In island operation only your power plant and power factor correction devices on your islanded part of the grid are providing power factor correction.

If you want to increase the power factor you need to add power factor correction devices to help correct the power factor when you operate in islanded mode, it is as simple as that.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: May 2009
Posts: 21
#3
In reply to #2

Re: Maintaining Power Factor

09/15/2009 6:43 AM

geb- Gujarat electricity board

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4

Re: Maintaining Power Factor

09/15/2009 9:03 AM

Where is the power factor meter sensing point? Is it looking at the transformer input? If so, when your power plant is running as an island, the meter is seeing only the unloaded transformer, and 0.2 is about right.

If your installation is similar to the drawing above, and CB "A" is open in island mode, the only load seen by the PF meter is the transformer. A transformer has very little resistance and a lot of inductive reactance. With no downstream load to add effective resistance, you will see a very low lagging power factor on the transformer input.

If the power factor is causing you to pay a penalty, you may want to consider deenergizing the GEB transformer (opening the input switch or CB) when in island mode.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6
In reply to #4

Re: Maintaining Power Factor

09/15/2009 3:25 PM

I believe this to be the spot-on diagnoses and suggested corrective action.

If the average PF is recorded separately, and not as kvarh, an unloaded transformer will certainly have this result. As kvarh, an unloaded transformer would not show up as a significant load/PF due to the insignificant load.

If you choose to de-energize the geb transformer, you may have to consider its' meter power source. It may not be permissible to de-energize the metering. Perhaps this is a question that you can get more desirable results from asking it of your geb service engineering staff.

CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5

Re: Maintaining Power Factor

09/15/2009 3:12 PM

The power factor is just a meaningless ratio without knowing what the load power is.

PF = 0.2 is not likely to me more than gost loading of negligible value. You are probably only feeding a transformer magnetizing inductance. What is the KW reading?

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amit_er1981 (1); CJMcGill (1); jack of all trades (1); marcot (1); pwr2thepeople (1); sb (1)

Previous in Forum: Pressure Transducers   Next in Forum: Current Transformer Costs

Advertisement