Voltage Problem

09/15/2009 7:28 AM

Dear All,

We have a gate office and guest house located about 1500m away from the source or MCC used to feed it the required power for its control and lighting.I have laid down PVC cable of 150mm2 for the route of 1500m with 4 joints in the way. The voltage at the required point is less than 300 V. Kindly suggest me options to get 380V line-line at the gate office.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Voltage Problem

09/15/2009 8:14 AM

You're stuck with either up-sizing the cable or transforming the source voltage to a higher value and reducing it at the load end.

Cable insulation rating will limit the amount you may raise the voltage.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru

Join Date: Dec 2008
Location: nj,usa
Posts: 1253
Good Answers: 33
#2

Re: Voltage Problem

09/15/2009 8:38 AM

When you say there are 4 joints in the way do you mean splices in the cable? Each splice will cause resistance.

I agree with BILL about starting with a higher voltage.But remember that if you raise the source voltage you will need to ensure that your cable is rated for that higher voltage. You may need to run a new cable. You can then use a transformer to step down the voltage at the gate office and guest house.

Good luck.

__________________
CARPE CRUSTULORUM!
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Voltage Problem

09/15/2009 10:12 AM

Your voltage is being dropped along the long length of the cable due to the conductor's resistance. You need to do the voltage drop calculation before selecting the cable. Find the resistance of the conductors from the cable manufacturer and calculate the voltage drop, the voltage drop shall be limited to a specified range (generally less than 5%). You already installed the cable – the solution now is to replace the cable with higher size or run more parallel cables to reduce the voltage drop.

Simple voltage drop calculation formula:

For Single phase: 2 x I x R x L

For three phase: 1.732 x I x R x L

Where, I = current passing through per conductor, R = resistance per unit length (meter or ft), L = length of the cable (in meter or ft)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Voltage Problem

09/15/2009 11:00 AM

How much load do you have at the site?

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 16
#5
In reply to #4

Re: Voltage Problem

09/15/2009 2:48 PM

Dear All, Thanks for ur response.

We have a step up transformer if I can install that in the one third of the way from the source or from the destination. The load at the guest house and the gate office is total about 125 A. Its tappings on the secondary side are 400V, 415V and 430V. Kindly suggest me is this the right way.

Best REGARDS

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6
In reply to #5

Re: Voltage Problem

09/15/2009 6:30 PM

WOW. You are trying to push a 125 amps through 0.932056788 miles of wire.

The utility would use 11 kv distribution line to do this. What is the name plate voltage output of the step up transformer? Need the voltage ratio to guess at the resultant voltage. You would connect the 300 volts to the 400 volt tap. Place the transformer at the guest house and not at the 1/3 point. The voltage will probably still be low.

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#8
In reply to #5

Re: Voltage Problem

09/15/2009 8:52 PM

You should lay a length of cable without any joint in between. There is always a waiting potential problem with those cables joint. If the cable joint is not done properly, it will caused heat generated at the cable joint point and increase your cable resistance in thus your voltage will drop. Heat generated at the cable joint will also able to damage your cable and most of the cable failure is at the joint portion.

Increasing the voltage in the network able to help up to a certain stage but increasing the voltage too much will also effect other electrical apparatus that is connected to the main distribution board.

What I can recommend is as follows

a) Check and measure your final output voltage at the end of the cable (Gate Office)

b) Conformed the final voltage at the end of the cable at your gate office.

c) Then calculate and installed a step up transformer at your gate office with protection such as MCCB for the primary side and ELCB or ZPCT (Zero Phase Current Transformer) for the secondary side of the transformer

Since your requirement of the power is about 380V at 125A, the step up transformer will be as follows;

a) Primary Voltage 300V (voltage at your gate office)

b) Secondary voltage will be 380V/400V/420V with 3 tapping

c) Step up Transformer power (KVA) = about 100 KVA (base on 420V calculation)

Since your cable is 150mm2, the current carrying capacity is about is 300 Ampere. Therefore, your primary step up transformer will be about 192 Amp (full load consumption) and your secondary side of your step up transformer, you can have the maximum current about 151A for 380V, 144.3A for 420V and 137A for 420V

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Voltage Problem

09/15/2009 6:47 PM

I read your last post wrong. What is the rating of the primary voltage? Do you have taps on the primary?

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#9
In reply to #7

Re: Voltage Problem

09/15/2009 10:16 PM

Before using the transformer, first try this:

  1. Measure the voltage at your Gate office without any load. I am expecting it is almost 380 V.
  2. Apply around 50% of load (60 A) and measure the voltage (assume it is 340 V)
  3. Apply as much as load up to full load (125 A) and measure the voltage (assume it is 300 V).

The voltage regulation of your Guest house to Gate office system is (380-300) x 100 / 380 = 21% (very poor)

Now if you use a transformer of 300V/380V at the Gate office, the output voltage will be ok (380 V) when there is full load. But if the load decreases (say 20% of full load, 25 A), then the drop across the cable will decrease to 20% ((80 x 25)/125 = 16 V only) causing the transformer input voltage increase to 364 V which eventually increases the transformer output voltage to 364 x (380/300) = 461 V. This voltage will be supplied to the 20% loads of the Gate office and you can think what will happen to these poor loads. If your load is guaranteed to be 100% all the times, then it may be ok, otherwise the voltage keeps increase with the decrease of loads.

So, think before proceed.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#10
In reply to #7

Re: Voltage Problem

09/15/2009 10:25 PM

Dear All, The tapping on the primary side is 380v

Register to Reply
2
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#11

Re: Voltage Problem

09/15/2009 11:43 PM

Wow I am very very impressed. Unfortunately impressed by the magnitude of your mistake, but impressed nevertheless.

If I am reading this right you have installed 1.5 km of 3-phase cable, so with a neutral thats 6 km of 150mm2 cable??

Way to go dude.

Back to solving this issue, you should not use a step-up transformer as has been pointed out, this will lead to excessive over-voltage at light loads. You will also get large voltage fluctuations as loads cycle on and off. This will inevitably lead to equipment malfunctions. You will need to use an RCD at your gate-house end, as the fault currents will be minuscule. I would suggest these fluctuations would play havoc with your RCDs too. (By the by, you need to generate the earth with a spike locally & use RCDs).

This equipment may be an answer:

http://www.ashleyedison.com/AC-Constant-Voltage-Drop-Compensator.htm

This device apparently provides a stable voltage output for varying inputs. I have never used this unit (and hope to never have to) but it exists nonetheless. A possible alternative could be a 100kVA UPS (with the added advantage of some battery backup) or even a VSD.

Or of course you could install another 6km of cable in parallel ;-)

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#13
In reply to #11

Re: Voltage Problem

09/16/2009 5:24 AM

GA especially this bit:-

you should not use a step-up transformer as has been pointed out, this will lead to excessive over-voltage at light loads.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#12

Re: Voltage Problem

09/16/2009 3:56 AM

Regards.

You have not mntioned the IP supply voltage & whether a single or 3 phase.

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 16
#14
In reply to #12

Re: Voltage Problem

09/16/2009 1:39 PM

dear All,

Thanx for your valuable discussion. I have checked today the voltage at the distribution board from where the guest house and the gate office will be fed. To my surprise with 70 percent load ON the voltages were LINE TO LINE 362V ac. Kindly suggest what can be the possible reason of this. Two days before at the same distribution board I was getting only 300V ac.May be the capacitor bank of MCC or source feeding to that distribution board put ON today by any supervisor without informing to anyone.

Best

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#16
In reply to #14

Re: Voltage Problem

09/16/2009 8:12 PM

If you want to boost up some voltage at your gate office, you can add some capacitor bank at your office DB Board. It will help to boost up about 15 to 20 volts.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#15

Re: Voltage Problem

09/16/2009 5:12 PM

If you added capacitors, that will definitely give you a voltage rise. See if you can get the size of the caps in KVAR. We can calculate the rise.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#17

Re: Voltage Problem

09/16/2009 9:58 PM

Simon

The voltage rise depends on the capacitor size. How did you get the 15v or 20 volts?

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 16
#18
In reply to #17

Re: Voltage Problem

09/16/2009 10:52 PM

Dear All, We are using the capacitor bank of 25 KVAR at the source. It might happen that the power factor improvement panel did not work and the voltages in the field were less. But now the voltages have been improved. Best Regards,

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#19

Re: Voltage Problem

09/16/2009 11:06 PM

Check the voltage at the source and see if it has increased.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#20

Re: Voltage Problem

09/17/2009 1:58 AM

egards.

Power Factor correction is not that simple to achieve a positive result unless you have the indicating of + & - power factor.

Or with Auto-Correction system installed

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 16
#21
In reply to #20

Re: Voltage Problem

09/17/2009 8:21 AM

Dear All,

we are going to install at the guest house the step up transformer that will help us to take the voltage from 362 V to 380V . The step up transformer has on its primry side the tapping of 380V and on the secondary side the tappings are 400V,415V and 430V.whts ur suggestions?

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#22
In reply to #21

Re: Voltage Problem

09/17/2009 8:32 AM

Check out buck-boost transformers. Here is an example.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 16
#23
In reply to #22

Re: Voltage Problem

09/17/2009 10:01 AM

Dear ,

We have already a one transformer of type step up and its tappings I have already mentioned. I will use it at Guest House.

Best Regards,

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#24
In reply to #23

Re: Voltage Problem

09/17/2009 11:29 AM

Be careful!

Is the load at the guest house constant? If not what do you think will happen to the voltage when the load is very small?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2009
Posts: 16
#25

Re: Voltage Problem

09/17/2009 11:44 AM

Dear Randall, Sometimes the load is very light when there is only 1 or 2 guests so I think the voltages will rise n may make a danger for the appliances what do u suggest now

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#26
In reply to #25

Re: Voltage Problem

09/17/2009 2:22 PM

I'm by no means an expert in this area, but:-

I'm afraid you only have two options, and both are expensive.

1.) Lay much thicker cable.

2.) Install high voltage cable; with a step up transformer at the source end, and, a step down transformer at the far end.

If you do a google search for "voltage drop calculator", and try some of the online calculators you will get a feel for the volts drop. I believe you should be trying to restrict it to less than 3%.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Score 1 for Good Answer
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AbrarAhmad (6); Anonymous Poster (1); BabyGuinness (1); Bill (2); Haajee (2); msamad (2); not so smart (1); Randall (3); Simon Wan (2); wareagle (6)

Previous in Forum: CT Classes   Next in Forum: NMD Calculations

Advertisement