Boiler Water Level Control

09/17/2009 3:38 AM

I am doing a boiler instrumentation up grade and would like to discuss the pro's and con's of using the different types of level control for safety and process control of boiler water level control. This plant has three types currently installed. Displacer type, Pressure differential, a Hydrastep which is a resistance type. Which are the best to use for each system?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Boiler Water Level Control

09/17/2009 11:11 PM

My understanding is that there must be 3 different types of level devices used together on a drum level for safety

Register to Reply
Commentator

Join Date: Dec 2008
Location: Young NSW Aust
Posts: 81
#2
In reply to #1

Re: Boiler Water Level Control

09/17/2009 11:33 PM

I suppose it depends which country you are in and its rules. In Australia we only have to have two types. One for level control and the other for a independant check.

Register to Reply
Anonymous Poster
#3

Re: Boiler Water Level Control

09/18/2009 12:18 AM

Here in Tasmania we use 3 types. One electrical transmitter that gives the level controller a PV, one non-electrical indicator that gives the operators a chance to see the level in a power outage or controlroom catastrophy, and one that is purely a selfcontained crash shutdown device that hopefully never comes into actuation that stops pumps/postitons vent valves ect. Of course there should be a sight glass at either end of the drum.

Rok

Register to Reply
Participant

Join Date: Jun 2009
Location: US/Angola, Africa
Posts: 2
#4

Re: Boiler Water Level Control

09/18/2009 3:00 AM

By using the Hydrastep which measures resistance between a probe and the wall of the enclosure, I think that the readings are more accurate than the displacer type because of of the density changes in the water due to the temp. Am I correct in this line of reasoning. I intend on using differential pressure type transmitter for my water level control and the Hydratstep for my safety shutdowns. Any comments or suggestions as I am not a Boiler specialist.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5
In reply to #4

Re: Boiler Water Level Control

09/18/2009 11:44 AM

It sounds like you've got a solid plan. The Hydrastep will be most accurate because its sensing is insensitive to temperature/pressure changes. The manufacturer's data sheet for the Hydrastep gives some impressive numbers:

"An independent report by Factory Mutual Research concluded that the probability of Hydrastep missing a trip condition is less than 1 in 300 million and that nuisance trips will be less than 1 in 10 million."

I'd bet on those odds.

The differential instrument should work well to give an analog input to the DCS. However, both the displacer and the differential can give erroneous readings when boiler conditions are outside of assumed values. It may be necessary to place level control in manual during startup, shutdown & large transients. That will have to be part of operator training.

If your installation is in the US, remember that the ASME Boiler Code requires both direct (gauge-glass) and indirect (instrumentation) level indication.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Boiler Water Level Control

10/15/2009 10:50 PM

Can ultrasonic level controls be usedon boilers? I have never seen it done, thought I would pose the question.

Register to Reply
Participant

Join Date: Nov 2009
Posts: 1
#7
In reply to #6

Re: Boiler Water Level Control

11/18/2009 9:54 PM

Theres is a system that uses Radar for level control and it is developed and Sold By Gestra If you would like more details please contact me

Cheers

Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Cajun_Sparky (1); Ozzzeee (1); pwr2thepeople (1); whezmabeer (1)