Capacitor Banks - Mode and Load

09/17/2009 7:32 AM

what we happen if 400 kvar cpacitor banks are on in manual mode and there is no load on mains ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jul 2009
Posts: 16
#1

Re: capacitor bank

09/17/2009 8:13 AM

happen in which sense? Do u want to know that if the voltages will improve or not? or do u want to know the power factor will improve or not?

Register to Reply
Anonymous Poster
#2

Re: capacitor bank

09/17/2009 8:24 AM

if there is no load, there is only reactive current. may be it is capacitive, but still it is reactive. The whole system works on that mode.

Register to Reply
Associate

Join Date: Apr 2009
Location: ras al khaima
Posts: 25
#3

Re: capacitor bank

09/17/2009 9:58 AM

then capacitor banks act as a load.

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4

Re: Capacitor Banks - Mode and Load

09/17/2009 9:13 PM

Your voltage will be charging your capacitor bank and you need to pay extra bill.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5

Re: Capacitor Banks - Mode and Load

09/18/2009 11:55 AM

hi!

You want to run 400 kvar capacitor bank ON on what kva transformer ?

if kva rating of transformer is < 750 - 800 kvar, there are chances, transformer winding shall burn.!

Of coure, you are happily paying for the CU losses at 400 kva load.

Further, over capacitance may bring resonance with transformer inductance, bringing over voltages across mains .

that is why, automatic correction panels being used for such a large applications.

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#6

Re: Capacitor Banks - Mode and Load

09/19/2009 8:27 AM

Your source will see a huge about 90 degee-off phase current load equal with the one you would be spared when used with the corresponding device it was matched with, but actually that will not be all losses (it's 90 degree off remember?) only a small part of it depending on the capacitor quality. Your wires up to capacitors will still be loaded though and will have losses too

__________________
Life is complex. It has a real part and an imaginary part.