Transformers and Impedance Percentages

09/17/2009 7:24 AM

On a transformer name plate %IZ(%Impedence) is mentioned. What is the meaning of %IZ and how it is calculated?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: % Impedance in transformer

09/17/2009 8:03 AM

Out put of transformer short circuited and input connected to some varying voltage until its output current equals to the rated current of transformer.

(some voltage/rated voltage)x100= %z impedance.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: % Impedance in transformer

09/17/2009 9:11 AM

Also see the previous posting http://cr4.globalspec.com/thread/41265

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Member

Join Date: Aug 2009
Posts: 7
#3

Re: Transformers and Impedance Percentages

09/17/2009 1:20 PM

By definition; The %impedence voltage is the three phase voltage expressed in percentage of the rated voltage, which when applied at one winding, with the other winding all three phases shorted (bolted), produces rated current in the winding to which voltage is applied.

If you are calculating it, it is nothing but impedance of primary plus impedance of secondary as measured at primary. The copper loss/coreloss parallel path also is to be considered, but effect is negligibel when calculating short circuit impedance as much lesser impdedance is in parallel.

Now the use of % impedence: The short circuit current through the trasformer is required for relay settings calculation, busbar/breaker adequacy calculation etc.

Say %Z of rated voltage drives rated current in primary and secondary winding. So if we apply full rated voltage it will be (1/%Z)x100 times the rated current.

For eg. If 20% is the impedance voltage of a transformer, then (1/20)x100=5 times rated secondary current would be the current from the transformer to a 3 phase fault at a bus directly connected to it.

Single phase to ground and three phase are also calculated some what in simillar way, but is more complex.

Hope clarifies.

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

msamad (1); rakesh_semwal (1); The electrical engineer (1)

Previous in Forum: MCCB Settings   Next in Forum: Capacitor Banks - Mode and Load

Advertisement