Impedance Voltage for a Transformer

07/30/2009 9:28 AM

Sir,

What should be the percentage of impedance voltage for 1000kva and 1250kva , 11kv / 433 volts Transformer, what is the effect on transformer if it changes below and above the standards ?

Please give full details regarding this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Impedance Voltage for a Transformer

07/30/2009 11:48 AM

dear,

you mean percentage impedence of a transfoermer ?

it seems you are in India. ?

Normally, as per minimum requirements of supply authorities, %Z of a transformer for 11kv designs is 5%. with IS tolerence of 10% +/- permissible.

Normally, 11kv 1000 kva / 12 50 kva transformers shall be designed with %Z of between 4.5% to 5.5%.

More the %Z of transformer, more Copper used for winding, increasing cost of the unit. But short circuit levels will reduce, mechanical damages to windings during short circuit shall also reduce. However, cost increases significantly with increase in %Z.

Lower %Z means economical designs. But short circuit fault levels shall increase tremendously, damaging the winding & core.

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Impedance Voltage for a Transformer

07/30/2009 10:13 PM

For a transformer, the 'Percentage Impedance Voltage' and 'Percentage Impedance (%Z)' mean the same thing.

The high value of %Z helps to reduce short circuit current but it causes more voltage dip for motor starting and more voltage regulation (% change of voltage variation) from no load to full load.

The effect of the low value is the other way around.

Bonus answer:

(from my previous post while I was a guest user: http://cr4.globalspec.com/thread/32420/Transformer-Impedance)

To measure the %Z, follow the steps below:

- Short the secondary side of the transformer with a current measuring device (Ammeter)

- Apply low voltage in primary side and increase the voltage so that the secondary current is the rated secondary current of the transformer. Measure the primary voltage (V1).

- Divide the V1 by the rated primary voltage of the transformer and multiply by 100. This value is the percentage impedance of the transformer.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: May 2009
Posts: 16
#3
In reply to #2

Re: Impedance Voltage for a Transformer

07/31/2009 5:12 PM

this is for single phase transformer what about 3 phase transformer?? say delta h.v star lv

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); hussam (1); msamad (1)

Previous in Forum: Calculating Losses in Transformers   Next in Forum: How to Select Cable Size For 7.5KW Induction Motor

Advertisement