Anonymous Poster

Isolation Transformer for Safety

09/18/2009 10:45 AM

Hello,

It's time for another stupid question! Today the subject is "using isolation transformers for safety".

I'm new in the big city and just fell off the electrcial cart. I'm having trouble visualising how an isolation transformer on an AC line helps reduce electrical shock. Say I have a 1:1 isolation transformer and I'm putting 120VAC in and getting 120VAC out. If I touch one output and Earth ground...why don't my ears smoke?

Is it because neither of the output lines have any reference back to Earth ground (which is often connected to Neutral in electrical distribution systems) because of the transformer? They're only 120V with regard to each other and 0V to Earth?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: Isolation transformer for safety

09/18/2009 11:21 AM

dear,

just draw the schematic diagram showing mains, neutral, isolation transformer, & out put power terminals of 120v ac.

did you got the answer ?

just observe that out put is isolated from neutral ( return path.) also, between mains & the load out put, impedence is added - of tr. coil. this reduces the fault energy significantly.

thiis is how, safety is increased. But you do get the electric shock ( lesser then that without the tr. ) if you touch live out put terminals with bare foot.

__________________
Exploring the Science of Electricity
Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#2

Re: Isolation transformer for safety

09/18/2009 11:36 AM

The trick is to remember that when we talk about Voltage, we really should be saying Voltage difference. That (the difference) is what it takes to make current flow. That's why birds can sit on a 50,000 V wire without getting fried; both feet are at the same Voltage (or very, very near) and no current flows through them. So, the isolation transformer has a 120 VAC output, but that is ONLY in relation to the other lead. There is no relation to ground.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#3

Re: Isolation Transformer for Safety

09/18/2009 4:57 PM

Hi Guest,

There is a variation on this theme and it involves there being a centre tap on the secondary which is taken to earth; under these circumstances the voltage between either of the output conductors and earth is 60 VAC. The description of such a transformer is therefore 60-0-60 on the rating plate. This form of transformer is popular with construction site temporary electrical systems for obvious reasons.

You should realise however that if your isolation transformer is connected to the mains via a residual current device (RCD) that it (the protective switch) will not operate in its earth leakage mode if faults occur on the secondary side of the isolation transformer. Therefore where as the proverbial shock protection of a 30mA RCD will work on the primary side you would not be afforded that protection on the secondary side circuits.

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#4
In reply to #3

Re: Isolation Transformer for Safety

09/19/2009 4:13 PM

Good answer, Massey. I think the guest does have a handle on the problem. I am going to get an isolation transformer eventually, 'cause they are supposed to be safer for working on electronic stuff. You will still get shocked if you get in between the two wires coming out of the transformer, I presume.

I did want to say, that on this side of the pond, I believe the RCD devices are called GFI, for Ground Fault Interrupting. Same rules would apply.

__________________
mike k
Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#5
In reply to #4

Re: Isolation Transformer for Safety

09/22/2009 5:29 AM

Hi mike k,

Thanks for the added info. at least you were able to get the gist of what I was saying.

Regards,

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Reply
Guru
Hobbies - Musician - Tube Amps Only Please!

Join Date: Apr 2009
Location: Los Angeles, California USA
Posts: 553
Good Answers: 1
#6

Re: Isolation Transformer for Safety

10/26/2009 11:33 PM

The secondary is isolated from the line voltage (primary) it works.

__________________
Regards, Maveric Manic - 'Knowledge is Power and Wisdom is knowing how to use it'
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

harry potter (1); Massey 726 (2); maveric_manic (1); mike k (1); TVP45 (1)