In many cases we base the ampacity on 1000 amps per square inch. Thats very safe. Conderations are silver or tin plated copper, round edge, square edge but copper is copper. I'm somewhat confused as to your panel current and my suggestion is, if you have a main c/b, size your cable accordingly. I don't think you're designing your own panelboard or maybe you are. The guys referred you to Storm Copper which is one of the big guys in copper bus bar mfg. They know their buscuits and as a switchgear designer, I use the IEEE-45, table A27 but as far as covering your ass, use 1000 amp/sq in.