Hi, i need some expert opinion on the UPS rating and capacity that my supplier proposed.
We have a few systems that should be wired to this 3-Phase UPS.
Ventilation fan = 3.7Kw
AHU fan = 2.8Kw
Freezer =1Kw
Other electrical appliances=1Kw
In total=8.5Kw
They have proposed that we should use a 10KVA 3-phase UPS and there are 32 batteries of 40AH each.
From the earlier thread, the calculation is as follows:
P/1.732*V*PF = I
Where
8500/(1.732*384*0.8)=15.98Amps
(384 is 12V*32 cells)
My supplier calculates it as (8500/(1.732*384))*0.8= 10.22Amps
May i ask which is correct?
They mentioned that 40AH means the battery is able supply 40A of power over an hour. For our current system running at 10.22Amps, the ups can support it for more than 30 minutes. It this correct too?