UPS Rating and Capacity

09/23/2009 9:05 AM

Hi, i need some expert opinion on the UPS rating and capacity that my supplier proposed.

We have a few systems that should be wired to this 3-Phase UPS.

Ventilation fan = 3.7Kw

AHU fan = 2.8Kw

Freezer =1Kw

Other electrical appliances=1Kw

In total=8.5Kw

They have proposed that we should use a 10KVA 3-phase UPS and there are 32 batteries of 40AH each.

From the earlier thread, the calculation is as follows:

P/1.732*V*PF = I

Where

8500/(1.732*384*0.8)=15.98Amps

(384 is 12V*32 cells)

My supplier calculates it as (8500/(1.732*384))*0.8= 10.22Amps

May i ask which is correct?

They mentioned that 40AH means the battery is able supply 40A of power over an hour. For our current system running at 10.22Amps, the ups can support it for more than 30 minutes. It this correct too?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Needed Help on 3 Phase UPS rating and capacity

09/23/2009 11:08 AM

Here is the calculation:

You didn't mention some important information such as UPS output voltage, load power factor, Inverter efficiency, allowable discharge voltage of batteries etc. Let's assume it:

UPS output voltage = 380 V

Power factor = 0.8

Inverter efficiency = 0.9

Allowable discharge voltage of batteries = 11 V (to obtain 40 AH from the batteries, the battery is allowed to discharge up to 11 V)

Based on your load, required UPS output current = 8500/(1.732 x 380 x 0.8) = 16.14 A

The minimum UPS size required = 8.5/0.8 = 10.6 KVA.

With 10% reserve capacity, you should select 12 KVA (or higher) size UPS.

12 KVA UPS output power = 12 x 0.8 = 9.6 KW

Your nominal DC voltage is 12 x 32 = 384 V. The minimum battery voltage = 11 x 32 = 352 V (when the load is on batteries and the batteries are discharged to the minimum allowable voltage).

The average discharge DC voltage = (384 + 352) / 2 = 368 V

The required input DC power to the inverter = UPS output power / Inverter Efficiency

(9.6 x 1000) / 0.9 = 10667 Watts

The Average Battery discharge current = 10667 / 368 = 29 A.

The required support time = 0.5 Hour

The Battery AH required = 29 x 0.5 = 14.5 AH

Considering 15% design factor and 25% aging factor, the actual battery AH required

= 14.5 x 1.15 x 1.25 = 20.84 AH

You have 40 AH batteries, so your battery capacity is enough to support even for 1 hour (based on the assumptions above).

For more detail, you can see the previous thread: http://cr4.globalspec.com/thread/38821#comment405933

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Needed Help on 3 Phase UPS rating and capacity

09/23/2009 11:32 AM

Hi MS, Thank you for the information.

I will contact my supplier to get the missing information. We were totally lost when they tried to explain to us on the rating and capacity.

This forum rockz !!!!! Cheers

Register to Reply
Member

Join Date: Jun 2009
Posts: 8
#3
In reply to #2

Re: Needed Help on 3 Phase UPS rating and capacity

09/23/2009 11:02 PM

Hi you mentioned you have a 1kW freezer. The compressor during start up will be 8 times the nominal current.

1000/380/1.732 = 1.51 Amps. x8 will be 12Amps.So you need to cater 12Amps for your freezer.

Otherwise during every compressor cycling (turning on and off) the UPS will go into Bypass for a split second.

During power failure, the first cycling will shut down the UPS due to an overload(as bypass is not available).

Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#4
In reply to #1

Re: Needed Help on 3 Phase UPS rating and capacity

09/24/2009 1:03 AM

Your calcs are correct but the OP has not expanded upon the base information.

Ventilation fan = 3.7Kw

AHU fan = 2.8Kw

These are output wattages. These fans are around 85% efficient at best. This equals 7.6 kW.

At 0.8 PF this equals 9.6 kVA.

Freezer =1kW

This is around 70% efficient at best. This equals 1.4 kW. But likely to have horrendous PF so at 0.6 PF this equals 2.4 kVA.

Other electrical appliances=1Kw

Lets take these at face value but at 0.8 PF this equals 1.25 kVA.

We now have a total of 10 kW & 13.25 kVA on the output. You can use these figures for your running.

So 10% reserve = 11 kW

90% eff = 12.2 kW

Note that UPS manufacturers typically use 0.8 PF for defining the output, so 12.2 kW = 15.3 kVA. Chloride, however, use 0.7 so for their machine 12.2 kW = 17.4 kVA.

The above can only be used for the run-time calculations. The start-up current of the motors will be 4-6 times their running current, but of course only for a few seconds. As mentioned in a later post, when bypass is avilable the UPS may flick to bypass to cope, but during mains failure bypass doesn't exist and the UPS will trip. Since this is obviously a high risk or emergency supply, you will need a much larger unit to cope.

Assuming our fans can't start together (which is unlikely to be correct but your call) the vent fan has a running current of about 8 amps (at 380V). Locked rotor current is going to be about 30-40amps. A 20 kVA UPS might cope, but you would be better with 30.

Note that the runtime of the UPS will be substantially unchanged; the larger capacity is purely to cope with motor start.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2009
Posts: 4
#5
In reply to #4

Re: Needed Help on 3 Phase UPS rating and capacity

09/24/2009 12:05 PM

Hi Everybody,

Thank you for the detailed explanation.

We are speaking to our contractor to get the information. We are still waiting for the reply.

We were unaware that there are so many factors to consider when buying an UPS. Through some googling we noticed that there is this term "non-linear high crest factor loads" which was discussed earlier.

We are hoping that the UPS comes with this Crest factor capability (some circuitry)which allow the inverter to be compatible with loads exhibiting a high crest factor. We are not sure if this is a good idea. Can someone kindly advise?

Cheers

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#6

Re: UPS Rating and Capacity

09/24/2009 1:29 PM

Hi Surfs,

My advice is to work out what you need and add half again. There is always things you never think of like lighting. Though I realise this is not a large item it really depends if you want to light just one corner of your factory or have everything working as normal? In which case and judging by what you need and the total number of cells. It may pay to get a Generator and perhaps a smaller version of an 'UPS'?

Just a thought.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Participant

Join Date: Sep 2009
Posts: 4
#9
In reply to #6

Re: UPS Rating and Capacity

09/27/2009 9:14 AM

Hi, generator might be a good idea. There might be a few seconds of down time which i am not sure how it will affect the airflow thru the facility. It is a safety requirement to keep the facility under -ve conditions at all times.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#7

Re: UPS Rating and Capacity

09/25/2009 3:01 PM

Just a thought.

If nobody is going to suffocate without ventilation during 30 or so minutes once a week, maybe provide with a modest UPS just the freezer (to save perisheables) and the "other" - needing its 1kW of power (lighting, working PCs, faxes, printers etc) ?

Register to Reply
Participant

Join Date: Sep 2009
Posts: 4
#8
In reply to #7

Re: UPS Rating and Capacity

09/27/2009 9:10 AM

Hi, there are some safety requirements for the facility. It is some how unique and ventilation is essential. Some thing like a BSL3 idea ...... . Contamination must be avoided.

For now, we imposed it on the vendor to provide a backup supply and UPS is one of their suggestion.

Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#10
In reply to #8

Re: UPS Rating and Capacity

09/27/2009 4:49 PM

Ah as I suspected and I will reinforce my post by saying you need a minimum of 30 kVA UPS.

One way to reduce motor start current is to use a VSD. However the UPS unfortunatley does not cope well with the harmonic currents generated and you end up back at square one, with a bigger UPS than you thought.

Now, a UPS converts the incoming AC to DC, then DC back to AC. The VSD works by converting the AC to DC, then the DC back to AC.....sound familiar?

What is needed is a UPS with built-in VSD. The VSD can be supplied direct from the DC bus. All problems get simultaneously solved. The batteries cope very well with short-cycle deep loads. Now why didn't I think of that?

Oh, I just did.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); babybear (1); BabyGuinness (2); kiansen (1); msamad (1); Surfs (3); Yuri B. (1)

Previous in Forum: Disadvantages of ONAN/ONAF against ONAN Transformer   Next in Forum: Knee Point Voltage and Current Transformers

Advertisement