KVA of UPS

06/07/2009 7:50 AM

what the relation between KVA of UPS & the load,,, how can we choose suitable UPS for SAitable load...

deos 40KVA,180 minute back up time suitable for hospital (150A maximum load)???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: KVA of UPS

06/07/2009 8:10 AM

150A, what voltage?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#2

Re: KVA of UPS

06/07/2009 8:16 AM

40KVA?- it depends on haw big is hospital and 180minuets?- again it depends on how long power fails in your area,

You should contact some local electrician and consultant.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: KVA of UPS

06/07/2009 3:42 PM

what the relation between KVA of UPS & the load,,,

P=VA

KVA = 1000 x VA

What is your normal expected current and load voltage?

__________________
jack of all trades
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4

Re: KVA of UPS

06/08/2009 2:25 AM

Does 40KVA,180 minute back up time suitable for hospital (150A maximum load)???

Not Possible.

Let make a simple calculation for your UPS back up time.

Assume your hospital is using 110 Vac Single phase

Total current for 40KVA = 40,000 / 110Vac =363.6 amp per hour

Hospital maximum load = 150 Amp

UPU back up time = 363.6/150 amp = 2hr 25.44 minute.

Of course, if your UPS is 100 % fully charged up.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Commentator

Join Date: Mar 2009
Location: Southern California
Posts: 97
Good Answers: 15
#6
In reply to #4

Re: KVA of UPS

06/08/2009 11:57 AM

"Total current for 40KVA = 40,000 / 110Vac =363.6 amp per hour"

Where did the "per hour" come from? Amps is a time-dependent measure already (Coulombs/second).

40KVA/110Vac = 363.6 amps, not amps per unit time.

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#8
In reply to #6

Re: KVA of UPS

06/08/2009 10:06 PM

Total current for 40KVA = 40,000 / 110Vac =363.6 amp per hour"

The above is just a simple calculation. Since we assume that the voltage is 110 V and the current is 150 Amp. Therefore, the total power is 16.5KW. For the power, we assume that the the power consumption by the load will be 16.5KW/h

Using the 40KVA UPS with battery back up, we assume that the UPS output will be 363.6 Amp per hr or 39.996 KW assuming no other losses. And since we also assume that the total power consume is 16.5KW/hr, therefore, the time that this 40KVA UPS can back up is about 2hr ++

Maybe my electrical terms or the calculation is not correct but I having been using this simple calculation to size up 20 over UPS in my factory and tested the back up time is 90% accurate.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Commentator

Join Date: Mar 2009
Location: Southern California
Posts: 97
Good Answers: 15
#10
In reply to #8

Re: KVA of UPS

06/09/2009 12:53 AM

"the total power is 16.5KW. For the power, we assume that the the power consumption by the load will be 16.5KW/h"

That is simply choosing an arbitrary length of time (one hour) as the unit of measurement. It does not make sense to express anything in terms of KW/hr. Since a watt is a Joule per second (J/s), referring to a KW/hr is basically saying a KJ/sec-hr, which is nonsense unless the system is increasing power exponentially over time. While the calculation may have worked on 18 of 20 UPS units in your facility, it is not a valid method of sizing a battery (as proven by the other 10% of the UPS's).

Instantaneous power is measured in watts; cumulative power consumption over time is measured in watt-hours, not watts per hour. Batteries for UPS's are selected to meet a desired amp-hour capacity. Thus total power consumption is limited by battery capacity, not the other way around.

Register to Reply
Participant

Join Date: Jun 2009
Posts: 4
#5

Re: KVA of UPS

06/08/2009 6:53 AM

full details of Load::

3 ph, 220\127VI\O , 60 Hz , 180min back up time,for NICU & ICU operation rooms for hospital.

what proper UPS to connect for this load???

alsoo there is Equation:: Amb = (KW*1000) \ (Volts * 1.73) ;;;;KVA=KW\power factor

so:: for 150A MDB ,,,KVA=60KVA

for 100A ,,,,KVA=40KVA.

thier is 40KVA, 180 min back time is available with me.....so how much does the load equal (Ampers) to be saitable with this UPS.

Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#7

Re: KVA of UPS

06/08/2009 4:14 PM

The rating of 40 kVA does not relate in any sense with the amount of time the UPS can provide power in case of a power failure, but the power (kW,kVA) requirement.

What matters is the quantity of batteries that are accessories to the UPS to store energy. You can order a 40 kVA UPS with batteries to provide 30 min, 45 min, 90 min, 600 min, etc of battery power (depends on how many batteries you install/connect).

Usually a UPS is installed to cover power requirements between losing the normal power grid and starting an emergency generator ( 30 sec - 10 min). Otherwise the volume of the required batteries is very big and space/ventilation/security problems appear

__________________
Scientes et audaces fortuna juvat !
Register to Reply Score 1 for Good Answer
7
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#9
In reply to #7

Re: KVA of UPS

06/08/2009 10:31 PM

Dear Eng_Tamimi

Here is the detail of the UPS design based on the following input data (some provided by you and some are assumed)

UPS Input Data:

Data provided by you:

Load current = 150 A

Phase = 3

Voltage = 220 V

Backup Time = 180 minutes = 3 hours

Assumed data:

UPS input voltage = 380 V, 3 phase

DC Voltage maximum = 130 V

DC Voltage minimum = 105 V

Average DC Discharge voltage = 115 V

Inverter efficiency = 85%

Charger efficiency = 90%

Battery Design factor = 15%

Battery Aging factor = 125%

Battery Charging time = 8 Hours (with 90% charged)

Battery Type = VRLA (Valve regulated lead acid)

Charger overload capacity = 20% for 2 hours

Battery cell max voltage = 1.33 V

UPS Design Details:

Inverter KVA (UPS KVA) calculation:

Required KVA = √3 x 220 x 150 = 57.2 KVA

You can go for the higher standard KVA which is 60 KVA UPS

Battery AH calculation:

Required DC side load = 60,000 / 0.85 = 70,588 Watts

Average DC load current = 70,588 / 115 = 613 A

Required Battery AH (Ampere Hour) = 613 x 3 = 1,839 AH

Considering design factor and aging factor, the actual battery AH required

= 1,839 x 1.15 x 1.25 = 2,644 AH

Number of batteries = 130 / 1.33 = 60

Charger Capacity Calculation:

Maximum discharged AH of the battery = 1,839 AH (in 3 hours)

90% of 1,839 AH = 1,839 x 0.9 = 1,655 AH

Battery charging current with this discharged AH = (1,655 x 1.1) / 8 = 228 A

(1.1 is a factor for Lead Acid type battery)

Charger output capacity = load current + charging current = 613 + 228 = 841 A

Considering charger overload capacity, required charger capacity = 841 / 1.2 = 700A

You need a charger of output capacity of 130V, 700A

Charger output watts = 130 x 700 = 91,000 watts

Charger input watts = 91,000 / 0.9 = 101,111 watts

Charger input current = 101,111 / (√3 x 380) = 154 A

Static Transfer Switch Calculation:

Static Transfer Switch should be capable of transfer with 20% overload of the UPS. So, the Static Transfer Switch capacity = 60 x 1.2 = 72 KVA

Bypass Transformer Capacity Calculation:

Bypass Transformer is generally should be 125% of UPS. So, the Bypass Transformer capacity = 60 x 1.25 = 75 KVA

Maintenance Bypass Switch Capacity Calculation:

The Maintenance Bypass Switch Capacity should be same as the Bypass Transformer. So, the Maintenance Bypass Switch Capacity = 75 KVA

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 7)
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#16
In reply to #9

Re: KVA of UPS

06/10/2009 7:16 PM

MS,

The calculation indicated is very intuitive. I have some questions about the correlation of some data:

1. The load power (UPS output), considering the values indicated, is 3 x 220V x 150A = 99 kVA, so the UPS should have a rating of at least 100 kVA, since the indication " a 100 kVA UPS means that the output power is 100 kVA.

2. I am assuming the input voltage is also 220/380V. Why did you indicate a DC voltage of 105-130V (this would represent 10 12V batteries in series) ? Normally that voltage should be close to the peak AC voltage, so in this case 220V. For the 60 kVA UPS in question, considering the DC voltage 220V, the current would be 70588/220=321A and thus, for a 3 hr time, the total battery capacity would be 3*321= 963 Ah.

3. The number of batteries is given as 130/1.33 = 60 (what do "130", "1.33" and "60" stand for ? (130V dc ?, 1.33 V/cell ?)

__________________
Scientes et audaces fortuna juvat !
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#17
In reply to #16

Re: KVA of UPS

06/10/2009 9:33 PM

1. The load power (UPS output), considering the values indicated, is 3 x 220V x 150A = 99 kVA, so the UPS should have a rating of at least 100 kVA, since the indication " a 100 kVA UPS means that the output power is 100 kVA.

It is √3 x 220 x 150 = 1.732 x 220 x 150 = 57.2 KVA

2. I am assuming the input voltage is also 220/380V. Why did you indicate a DC voltage of 105-130V (this would represent 10 12V batteries in series) ? Normally that voltage should be close to the peak AC voltage, so in this case 220V. For the 60 kVA UPS in question, considering the DC voltage 220V, the current would be 70588/220=321A and thus, for a 3 hr time, the total battery capacity would be 3*321= 963 Ah.

The DC voltage not necessarily has to be close to peak AC voltage. The chargers are most often built with input transformers to convert the input AC voltage to the required voltage level (similarly, the inverters are also built with the output transformers). You also could design it with a 220 V DC system, in this case you have less AH but need more number of cells in series. Generally the industrial UPS DC system is between 140 V (max) to 105 V (min) with nominal operating voltage 130 V.

The DC voltage varies, especially when the UPS is run on batteries. The batteries get discharged and the DC voltage is decreased - vice versa when batteries get charged.

3. The number of batteries is given as 130/1.33 = 60 (what do "130", "1.33" and "60" stand for ? (130V dc ?, 1.33 V/cell ?)

Sorry, it should be 'Number of cells = 140 / 2.33 = 60'.

Here, 140 is the maximum DC voltage, 2.33 is VPC (voltage per cell) and 60 is the number of cells. Generally, the VPC of VRLA cells is max 2.33 and min 1.75. When the cells are discharged to the min VPC level, the DC voltage becomes 1.75 x 60 = 105 V.

Hope it is clear now.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#18
In reply to #17

Re: KVA of UPS

06/11/2009 12:25 PM

MS,

1.The referenced 220V voltage is line-to-line voltage, since the system is 220/380V, so it should be either 3 x 220 x 150 or sqrt(3) x 380 x 150.

2.I understand the reasoning of 140V but based on what I found out from UPS industrial manufacturers (APC, MGE, etc) the DC voltage was the one I mentioned.

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#20
In reply to #18

Re: KVA of UPS

06/11/2009 6:44 PM

1. Yes, you are absolutely correct if 220 V is line to neutral.

2. Thanks for this information. Just one more important thing to clarify - for higher DC voltage, the larger number of cells is connected in series. A problem in one cell causes problem in the DC voltage system. However, the battery cells are now more reliable than it is used to be.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#19
In reply to #17

Re: KVA of UPS

06/11/2009 12:26 PM

MS,

I misspelled in my previous response: 220V is line-to neutral voltage, 380 is line-to-line.

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Associate

Join Date: Aug 2008
Location: Nigeria, West Africa (+1 GMT)
Posts: 46
#22
In reply to #9

Re: KVA of UPS

10/05/2010 5:13 AM

Hi MS

considering a Depth of Discharge (DoD) of 60%, what would be the required battery AH for this scenario?

Br,

EnB

__________________
One good Thing deserves Another
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#23
In reply to #22

Re: KVA of UPS

10/05/2010 7:44 AM

Hi EnB,

I can put no figure/s on the DoD or Ah needed.

For a hospital or any other situation which MUST have power, the power needed differs from one situation to another, and with a hospital, they would, I imagine have several UPS and several generators to cope. This will obviously vary from a very large hospital to a relatively small one also!

The basic rules of thumb as issues and posted by others on this thread, of how to work out the UPS necessary will still apply. You must have or figure out the 'NEED' for power and for how long that need is likely to be before an UPS of the correct sort can be installed.

I realise you may be learning, or wanting to find out these details, but, until, and when you are trained to install these UPS in power hungry situations of many thousands of Volts, 'guessing' or 'trying to figure out what is necessary' should be left to those who know what they are doing and can advise correctly and safely in these situations. No offence intended.

I suggest you write to the IEEE. Try this search site for life-critical situations and Hospitals in particular:

http://www.google.co.uk/search?q=IEEE+UPS+hospitals&ie=utf-8&oe=utf-8&aq=t&rls=org.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#11

Re: KVA of UPS

06/09/2009 12:55 AM

Hello eng tamimi,

I cannot see that this UPS situation can be applied to a hospital. There is no need for it with regard to hospitals because, each hospital has its own power supply back up. That is how things are in the UK anyway.

A hospital has hundreds of computer driven electrics, many of which are directly used to save lives. So the hospital needs a power supply which is not going to fail.

I hope this answers your question?

I cannot see this question has any relevance to computers running in any one hospital.

bb

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Participant

Join Date: Jun 2009
Posts: 4
#12
In reply to #11

Re: KVA of UPS

06/10/2009 6:49 AM

dear mr. babybear

u are right, but for more safe and to be far from power problem; we use UPS.specially in critical loads in Hospital as ICU & NICU.

Register to Reply
Participant

Join Date: Jun 2009
Posts: 4
#13
In reply to #12

Re: KVA of UPS

06/10/2009 7:00 AM

dear, Mr. msamad

surely, best answer

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#15
In reply to #12

Re: KVA of UPS

06/10/2009 7:04 PM

eng tamimi,

Thank you for your reply post.

Under those circumstances it perhaps make sense. But with only three hours standby, you had better hope and power cut with be less than that?

Take care

bb

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Anonymous Poster
#14
In reply to #11

Re: KVA of UPS

06/10/2009 5:42 PM

In the USA hospitals have redundant generators. Generators have to start and come- up to frequency and voltage during a power outage before the ATS will transfer the load, hence the need for UPS for loads that cannot sustain an outage of even a few seconds. If there are generators, then UPS battery time can be short. 15 minutes should be good insurance. Be sure to commission to be sure the UPS will accept the generator's output.

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#21
In reply to #14

Re: KVA of UPS

06/11/2009 7:04 PM

Hello Guest,

In the USA hospitals have redundant generators. ..............................Generators have to start and come- up to frequency and voltage during a power outage before the ATS will transfer the load,

hence the need for UPS for loads that cannot sustain an outage of even a few seconds.

I never thought of about that. Of course every ward and Theatre has all kinds of electronics installed these days and some sort of system, as you describe, has to be used!

bb

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: