Negative Pressure in Kiln / Afterburner?

09/25/2009 1:05 PM

Hi

I'm new to the instrumentation game, and I have to monitor the negative gauge pressure in a rotary kiln and afterburner, with temperatures at 1100 Celsius and 1700 Celsius, respectively. Any ideas about the type of sensors and accessory equipment best suited for the job. Readings will need to be looped to a plc.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#1

Re: Negative Pressure in Kiln / Afterburner?

09/26/2009 12:40 AM

Use tubing to carry the pressure out to to a friendlier location. At 1700°C, you might have to use ceramic tubing.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: May 2007
Location: Ohio. USA
Posts: 578
Good Answers: 30
#2

Re: Negative Pressure in Kiln / Afterburner?

09/26/2009 3:21 PM

Since you are measuring vacuum if all goes right the heated gas does not get to the gage. Like dkwarner said connect it with a length of tubing. I have several vacuum sensors in a similar application that work fine. The tubing should be long enough or of a material so as to not conduct the heat to the gage. With a length of small tubing and no leaks at the gage this could maybe even tolerate short times at a positive pressure.

__________________
Everything I know about opera I learned from Bugs Bunny
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#3

Re: Negative Pressure in Kiln / Afterburner?

09/28/2009 3:31 AM

Attention: Ceramics have in general a high thermal conductivity so that the length has to be quite big till you reach an acceptable temperature.

The best solution could be a double tube with an air cooling flow between the two components and at the end a tube of SS which has a lower thermal conductivity and could be shorter. To make it shorter you could use fins when the tube is outside of the hot chamber.