Over All Screen and Individual Shield termination in Marshalling

09/26/2009 1:23 AM

Gentlemen,

I have a query regarding the concept of Instrument Over all and individual shield (i am talking about multipair cables ofcourse).

For example if we have a lets say 24 pair cable with OAS and IS both (and the field end is not connected and kept open to avoid ground loop in this case) , the IS will definitely be connected to the Instrument Reference Ground Bar within the Marshalling Cabinet. My confusion is about the overall screen of the cable "WILL THE OVER ALL SCREEN BE CONNECTED TO THE INSTRUMENT REFERENCE GROUND OR THE POWER SAFETY GROUND WITHIN THE CABINET ? "

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#1

Re: Over All Screen and Individual Shield termination in Marshalling

09/26/2009 11:56 PM

Signals are never connected to power safety ground. perhaps a shield to transformer can be connected to power safety ground. In case casing is power safety ground connected then all signal ground need to be isolated from instrument case. If signals are differential type, then they can have common ground reference even at higher potential and common mode rejection can remove the elevated DC portion.

If you are sure that signal ground and power ground are very near to each other then the power ground can be connected to signal ground through paired diodes to keep a maximum difference of +/-600mV maximum from power ground. For signal levels very small this to be avoided.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#4
In reply to #1

Re: Over All Screen and Individual Shield termination in Marshalling

09/28/2009 12:15 AM

Regards.

A GA for proer reply.

I would like to add that it should only b on one point ONLY not on both ends of cable.

Register to Reply
Anonymous Poster
#2

Re: Over All Screen and Individual Shield termination in Marshalling

09/26/2009 11:57 PM

Both Overall and Individual screen shall be connected to Instrument Earth bar in the Marshalling cabinet.

Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#3
In reply to #2

Re: Over All Screen and Individual Shield termination in Marshalling

09/27/2009 7:12 AM

This may be OK in electrical wiring but not in instrumentation where power ground and signal ground are separated by isolation and this comes with price. See how they do it at www.dataforth.com/

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Haajee (1); Shyam (2)

Previous in Forum: Negative Pressure in Kiln / Afterburner?   Next in Forum: day tank instrument to avoid oil overflow

Advertisement