SF6 Vs Vacuum

09/27/2009 1:06 AM

Dear Friends,

Pls eloborate the advantages & disadvantages of SF6 & Vaccum Circuit Breakers.

Regards,

Manimaran.V

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#1

Re: SF6 Vs Vacuum

09/27/2009 1:34 AM

i suggest you attend the National Seminar on Recent Developments in Switchgear . . . . at Mumbai on 9th and 10th October 2009 - organized by the Academy of Resources Management

Register to Reply
Active Contributor

Join Date: Sep 2009
Location: Pakistan
Posts: 11
#3
In reply to #1

Re: SF6 Vs Vacuum

09/28/2009 1:20 AM

kindly give further detail of event. web address and prereq of seminar as mentioned by Fatehi

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#5
In reply to #3

Re: SF6 Vs Vacuum

09/28/2009 1:38 AM

All India Seminar " SWITCHGEAR – RECENT DEVELOPMENTS "

( 09th & 10th October, 2009 )

Prof. R. Chatterjee (Chairman)

Academy of Resource Management

11, Maya Apartments, Plot No. 467, TPS - III, 14th Road, Khar (W), Mumbai - 400 052.

Phone : - +91 9820656206 / +9122 2600 2966

academyresource@yahoo.com academyresource@gmail.com

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#2

Re: SF6 Vs Vacuum

09/27/2009 11:55 PM
__________________
Per Ardua Ad Astra
Register to Reply
Anonymous Poster
#4

Re: SF6 Vs Vacuum

09/28/2009 1:31 AM

Dear manimaran,

go through the following .

Sulphur hexafluoride (SF6) is an inert, heavy gas having good dielectric and arc extinguishing properties. The dielectric strength of the gas increases with pressure and is more than of dielectric strength of oil at 3 kg/cm2. SF6 is now being widely used in electrical equipment like high voltage metal enclosed cables; high voltage metal clad switchgear, capacitors, circuit breakers, current transformers, bushings, etc. The gas is liquefied at certain low temperature, liquefaction temperature increases with pressure.
Sulphur hexafluoride gas is prepared by burning coarsely crushed roll sulphur in the fluorine gas, in a steel box, provided with staggered horizontal shelves, each bearing about 4 kg of sulphur. The steel box is made gas tight. The gas thus obtained contains other fluorides such as S2F10, SF4 and must be purified further SF6 gas generally supplier by chemical firms. The cost of gas is low if manufactured in large scale.


Medium-voltage circuit breakers rated between 1 and 72 kV may be assembled into metal-enclosed switchgear line ups for indoor use, or may be individual components installed outdoors in a substation. Air-break circuit breakers replaced oil-filled units for indoor applications, but are now themselves being replaced by vacuum circuit breakers (up to about 35 kV). Like the high voltage circuit breakers described below, these are also operated by current sensing protective relays operated through current transformers. The characteristics of MV breakers are given by international standards such as IEC 62271. Medium-voltage circuit breakers nearly always use separate current sensors and protection relays, instead of relying on built-in thermal or magnetic overcurrent sensors.

Medium-voltage circuit breakers can be classified by the medium used to extinguish the arc:

Vacuum circuit breaker—With rated current up to 3000 A, these breakers interrupt the current by creating and extinguishing the arc in a vacuum container. These are generally applied for voltages up to about 35,000 V, [4] which corresponds roughly to the medium-voltage range of power systems. Vacuum circuit breakers tend to have longer life expectancies between overhaul than do air circuit breakers.
Air circuit breaker—Rated current up to 10,000 A. Trip characteristics are often fully adjustable including configurable trip thresholds and delays. Usually electronically controlled, though some models are microprocessor controlled via an integral electronic trip unit. Often used for main power distribution in large industrial plant, where the breakers are arranged in draw-out enclosures for ease of maintenance.
SF6 circuit breakers extinguish the arc in a chamber filled with sulfur heaxafluoride gas.
Medium-voltage circuit breakers may be connected into the circuit by bolted connections to bus bars or wires, especially in outdoor switchyards. Medium-voltage circuit breakers in switchgear line-ups are often built with draw-out construction, allowing the breaker to be removed without disturbing the power circuit connections, using a motor-operated or hand-cranked mechanism to separate the breaker from its enclosure.

Register to Reply Off Topic (Score 4)
Participant

Join Date: Jun 2009
Posts: 1
#6

Re: SF6 Vs Vacuum

09/28/2009 1:48 AM

Dear Manimaran,

Hope you are in ABB. We are using the ABB SF6 breakers in 400kV switch yards. You can very well look into the specs. In my opinion, the SF6 are best suited for EHV. We use it for 33kV, 66kV, 230kV & 400kV S/S. We widely use the VCBs in 11kV panels indoor & as field VCBs. Bye.

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: SF6 Vs Vacuum

09/28/2009 11:15 PM

best would be to call ABB and enjoy the fun if they respond to your call.

crm

Register to Reply
Anonymous Poster
#13
In reply to #7

Re: SF6 Vs Vacuum

06/21/2010 3:19 AM

This is 200% correct . No response , no call from ABB ,

Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#8

Re: SF6 Vs Vacuum

09/30/2009 4:09 AM

Dear Sh.Manimaran,

1)At the outset it is to be noted that in the case of VCB -breaker the making and breaking action takes in Vacuum medium, while in the case of SF-6 breaker the same takes place in SF-6 medium.Accordingly these are named as VCB or SF-6 Breaker.

2)The insulating strength of SF-6 gas in the case of SF-6 breaker is much higher than that of vacuum used in VCB.

3)It is due to this high dielectric strength of SF-6, Sf-6 breakers are used above 66KV system ie 66Kv,132KV,220KV and 400Kv systems as breaker applications.

4)VCB breakers are normally used and economical upto 33KV system.

5)SF-6 breaker also used for 11Kv and 33Kv system

6)VCB breakers are economical compared to SF-6 breakers.in lower range upto 33kv

7)In SF-6 breaker there is no maintnance except occassional gas leakage filling whereas in VCB the no of operations of breaker are limited and VCB bottle has to be replaced.

Finally SF-6 breaker scores over to VCB in all voltage ranges due to NIL maintenance ,excellent insulating properties and economy.

Regards

V.Ambarani

===================================================================

__________________
Best Regards
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#9

Re: SF6 Vs Vacuum

09/30/2009 4:17 AM

Sh.Manimaran,

1)At the outset it is to be noted that in the case of VCB -breaker the making and breaking action takes in Vacuum medium, while in the case of SF-6 breaker the same takes place in SF-6 medium.Accordingly these are named as VCB or SF-6 Breaker.

2)The insulating strength of SF-6 gas in the case of SF-6 breaker is much higher than that of vacuum used in VCB.

3)It is due to this high dielectric strength of SF-6, Sf-6 breakers are used above 66KV system ie 66Kv,132KV,220KV and 400Kv systems as breaker applications.

4)VCB breakers are normally used and economical upto 33KV system.

5)SF-6 breaker also used for 11Kv and 33Kv system

6)VCB breakers are economical compared to SF-6 breakers.in lower range upto 33kv

7)In SF-6 breaker there is no maintnance except occassional gas leakage filling whereas in VCB the no of operations of breaker are limited and VCB bottle has to be replaced.

Finally SF-6 breaker scores over to VCB in all voltage ranges due to NIL maintenance ,excellent insulating properties and economy.

Regards

V.Ambarani

===================================================================

__________________
Best Regards
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#10

Re: SF6 Vs Vacuum

09/30/2009 5:12 AM

how green are SF6 breakers compared to vac breakers?

Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
Good Answers: 3
#11

Re: SF6 Vs Vacuum

10/04/2009 11:37 AM

What Ambarani wrote were mostly correct and I have something to add in answering your simple question.

1.In my opinion,at the time when the manufacturing of oil circuit breakers started to decline,European MV (11,22 KV) manufacturers mostly went into the developement SF6 CB while the Japanese and some US manufacturers went into VCB technology.Westinghouse,Toshiba,Meidensha,Mitshubishi,Aichi,Toyo Denki who make their own vacuum interruptors were the early ones.European manufacturers such as Siemens Germany,Brush UK were much later in manufacturing 11/22/33kv VCB.

ABB started using BBC's Carlo Emag 11kv VCB when ASEA and BBC merged in Europe.The ABB vacuum interruptor (where the normal or fault currents are broken/interrupted ) was manufactured in Ratingen(I forgot the spelling) near Duseldoff,Germany.ABB have been buying so many other switchgear and transformer companies all over the world that ABB's Engineers have a lot to study and learn on/about ABB's own products if they want to be competent and confident in giving the right technical imformation/answers.Otherwise,they just do not response.

2.The sucess and survival of any MV switchgears depends mainly on 2 major primary reasons,(A) Engineering/Technical Functionality,reliability,safety etc (B) Costs.

For example,11kv VCB panel is between 600 to 700 mm wide for almost any manufacturer in the world because almost everyone is dependent on the dielectric strength of (atmospheric,humid)air as the insulating medium for the conductor parts(main busbars,dropper bars,CT,PT,cable terminations etc) outside the vacuum bottles.800 to 900mm W for 22kv and 1200 W for 33kv. This is also true for SF6 CB panels.The distance needed by the copper-chromium alloy main contacts in the 11kv vacuum interruptors for the arc to be extinguished is a travel of about 12 mm.The time to interrup or break is about 50 milli seconds.This distance and time are much longer in SF6 interruptors.

To assist in the quick extinguishing of the electric arc,different manufacturers uses different designs and arrangements.A simple and effective design in vacuum interruptors of VCB is "flat main round centre with spiral star fingers" Cu-Cr contacts.The lines of arcs which are actually HV currents in electron/plasma state travel from one surface to the other and repelling each other with the self generated concetric magnetic fields.These lines of arcs diminishes as it rotate and move away from the circular contact center.All these happen in 50 mSec in a gap of 12mm.The ionised plasma,vapour of copper will stick onto the stainless steel cylindrical sheet as solids while cooled,which is placed a little away from this contacts.The hermatically sealed vacuum bottle thus maintains its degree of vacuum.For normal current switching,most Japanese VCB interruptor are garanteed for 10,000 times of switchings and 10 to 20 times of switching at fault current levels before you need to change any vcb bottle which should not happen in 30 to 40 years of usage.

In SF6 interruptors,"puffer" arrangement is used to pump SF6 gas and blow across/along the path of the arc to quench and "draw/lengthen"the arc so as to extinguish it while the main contacts are moving away from each other.The SF6 gas is about 6 times heavier than air and its molecules can break and recombine and help to dissipate the arcing heat in the process.However, I have not seen any SF6 manufacturer matching the VCB'garantee of 10K In and 20K no current switching life.

For 11/22kv SF6 CB ( and RMU),the tendency is for a manufacturer to put the complete 3 pole switching/breaking contacts in a single common SF6 gas tank as all the live parts can be place closely together and minimise gas leakage by using one common actuating sharft instead of 3 individual sharfts for each pole.This arrangement contradict phase to phase segregation of some specification.Extremely minute gas leakage is happening all the time,mainly through the "o"ring gas seal on the actuating shaft,gas filling valve,gas pressure meters/sensors and through the wall of the steel tank plate! to minimise this, stainless steel tank(where costly welding in inert gas enviroment is required) and lower gas pressure (1.1 atmosphere ) designs are employed thus limiting the miniturisation effort.SF6 is Sulphur hexa floride where florine is a helogen gas which is not good for the ozone layer.This is a small quantity compared to hair spray and tyre/furniture polish sprays for example.

3.SF6 switchgears using vacuum interuptors are the interesting designs taking advantage of the characteristics of the two.

In 33kv level indoor/outdoor switchgears where in ABB's design,3 single vacuum interruptors are placed in a common SF6 tank and the main bus bars chamber,dropper bars and Primary sides of CT PT are in another chamber,the cable termination requires single core cable which has expensive and elobrate epoxy molded parts and copper and rubber seals to make it air tight.For circuit and busbar isolation one has to operate the 2 isolating switches,one above one below vcb, in side the main gas tank via a seperate shaft as the CB is non withdrawable physically.The one advantage for this design is that it is less than 700mm wide as compared to 1200 or 1300 mm W VCB panels and it is sealed off from its enviroment.The disavantage is high costs.In most commercial,public and industrial projects,one can place the bigger and cheaper 33KV VCB in the less expensive floors/levels.Siemen has individual phase gas insulated,vacuum interruptor CB design.

4. Eventhough SF6 can easily cover the whole range of CB from 11kv to EHV. The original strong believer of SF6 gas only CB manufacturers had no choice but to eventually involved in the design and manufacturing of VCB for 11KV to 33KV range.In this range,VCB has the distinct advantages of simplicity,reliability,low maintenance,lower costs in itself and cable/termination.The ease of extension and coupling to alternative make but similar designs,thus cheaper future extension thus it needs no spare panels at the on set of the project.

As a consulting or consummer engineer considering the economic and technical advantages,I choose VCB in MV.

Best regards,

Khor

Register to Reply
Anonymous Poster
#12
In reply to #11

Re: SF6 Vs Vacuum

11/06/2009 4:21 AM

Excellent chap ,you are too educative on SF6 and VCB.I concur with you,VCB is the way economically,financially,environmentally and technically.

Thanks

Eng.ole Khabi

Register to Reply
Anonymous Poster
#14
In reply to #12

Re: SF6 Vs Vacuum

07/29/2010 4:29 AM

Dear Guest,

Your jumping to conclusion to VCB as better over SF6 is a hasty and decision based on without proper technical understanding.

You seemed to have some negative mktg skills and are groomed too do the same.

ABB has been targetted by few competitors and they go to very negative limits.

Even I was also working in such company earlier where whole orgainsation used to work on proving VCB better against SF6. Whereas the true VCB technology promoter - Siemens never worked on negative mktg and they enjoy high level of customer preferences and have their own market share.

Don't work for company , work for yourself and think as an engineer. You shall earn your reputation based on the same wherever you go in the world.

Register to Reply
Anonymous Poster
#15
In reply to #14

Re: SF6 Vs Vacuum

08/07/2010 8:39 AM

Dear Guest,

I wrote this article based on many years of direct working experience under varied applications,as a manufacturer,end user,electrical consulting engineer,project and maintenance engineer and trading of varous makes of VCB and SF6 switchgears.I did not give more points or details / type test reports as I was/am not in my home country and do not intend to do that.I am not with any big company at the moment.

I sincerely hope and will be very grateful that you or any kind engineer/technician can provide all of us with more unbiased in-depth technical and economical comparisions on this topic so that others and I may share this knowledge in CR4 forum.Economical in terms of the use of material,space,insulations,interchangeability,safety,cost,and time.I value engineer who can understand and evaluate based on engineering data and imformation and can form his/her own opinion/stand.Some do not and cannot.

Both ABB and Siemens have VCB and SF6 switchgears.

Best regards,

Khor.

Register to Reply