Anonymous Poster

LPG

09/27/2009 9:28 AM

Can anyone tell me if IP67 rating is suitable for a zone 2 area using propane?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: LPG

09/27/2009 3:04 PM

If you are just planning on sticking standard IP67 rated industrial gear or standard industrial gear in an IP67 enclosure and mounting it in a Zone 2 area then no it isn't.

You will need to buy suitably rated and certified hazardous area equipment or mount the standard industrial equipment outside the zone in the safe area.

__________________
jack of all trades
Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: LPG

09/27/2009 9:45 PM

IP is for 'Ingress Protection', it is not for the explosion proof designation. IP designation of an enclosure is the degree of the protection from the intrusion of the environmental solid objects and liquids into the enclosure (see http://www.neteon.net/RefDnFiles/IP%20Rating%20Reference.pdf for details). IP54 should be enough protection in this case. I worked in a refinery in the heavy rain fall and dusty area. We used IP54 for outdoor equipment and had never problem.

The explosion proof equipment protects the out side explosive environment from the inside explosion of the equipment. All electrical equipment that is used in the hazardous area (Zone 0, 1 or 2) must be explosion proof. In the case of propane, the equipment designated as EEx d IIB T4 (IIB for gas group for Ethylene and temperature code T4 for 135 degree C) should be enough, however consult an expert before select the equipment. For propane, you even can select lower grade of explosion proof such as EEx d IIA T1 (IIA for gas group for propane and temperature code T1 for 350 degree C). The gas group indicates that the internal explosion can occur with the type of gas indicated and the temperature code indicates that the equipment surface temperature will never goes beyond the indicated temperature when the external explosion occurs. The 'T' code should be selected in such a way so that the flash point of the gas is higher than the temperature of T code. The selection, especially the letter 'd', also depends on the equipment you are selecting – it could be also i or e instead of d.

All these above are per IEC (European) standards. If you are in North America, then the designations are different. You have to select the equipment per the NEMA enclosure protection and NEC 500 explosion classification.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: LPG

09/28/2009 12:09 PM

Zone 2-suitable installations for propane must be used within the zone. EEx ib installations with IP00 rating would be suitable, for example. EEx d equipment and cable glands may only have a rating of IP55. EEx e junction boxes might be IP66 even if IP68 glands are fitted.

The way the question is asked would suggest that the best course of action would be to consult a local qualified electrical designer to specify and select the best course of action and suitable equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: LPG

09/29/2009 6:13 AM

YES! YES oh YES it is!

Do it! Do it!

They haven't had anything good on the "Engineering Disasters" channel lately.

Reply Score 2 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5
In reply to #4

Re: LPG

01/01/2010 7:24 AM

Well I guess he didn't take your advice, been watch the "disaster channel", nothing so far

__________________
The square root of nothing is what you make it!
Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (1); jack of all trades (1); msamad (1); PWSlack (1)