Neutral Wire Missing

09/30/2009 7:05 AM

How should I connect a Surge Protection Device (SPD) with 4-wire + ground (wye) if the neutral wire of the electrical system is not available? Should I just splice the neutral & ground lead wires of the SPD together and connect them to the grounding system? Or should I just use a delta (3-wire+ground wire) SPD?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Sep 2009
Posts: 99
#1

Re: Neutral Wire Missing

09/30/2009 11:35 PM

If there is no neutral available then do NOT USE A 4 wire SPD! I repeat do not use a 4 wire SPD on a 3 wire system. A 4 wire is designed with the neutral in mind for any surge or spike. This is like having an arc fault and the current exceeds fault current rating on a electrical breaker. It will blow it's self up and cause more damage to the sytem. Get the right one, there is a reason they have a 3 wire SPD

-Woz-

10 Years Of Electrical Installation in Industrial setting

Electrical Eng. for 5 years

Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2009
Posts: 3
#2
In reply to #1

Re: Neutral Wire Missing

10/01/2009 12:42 AM

Thanks kwoznia 1 for the reply. However, let me clear that they do not have a 3-wire system (delta). I checked the voltages, they are for sure in wye (4-wire + ground, L-L is 470v, L-Ground is 271v). The problem is there is no neutral wire at the circuit breaker (or anywhere) where I have to install the SPD. Are you suggesting that I should not use an SPD designed for wye (and just have the neutral & ground lead wires of the SPD spliced together and connect them to the grounding system of the building) and instead use a 3-wire, delta-designed SPD? Please reply as soon as possible. Thanks again.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3
In reply to #2

Re: Neutral Wire Missing

10/01/2009 12:58 PM

Rossmmac,

There are 2 different types of surges to consider: voltage & current.

The SPD should clamp line voltage and drain any excess through the ground terminal, not the neutral. The design is based upon the rated line voltage, so you should be fine there as long as the SPD nameplate agrees with the service design.

For current surge protection the answer is less certain, because a 4-wire device is designed with a neutral wire in mind to carry part of the total energy transfer. The current limiting circuitry may not have the capacity to drain all the energy through only 3 terminals. However, if the peak phase current and energy dissipation ratings are sufficient for anticipated faults, you may be okay.

All of this is with the caveat that I don't know the brand/model/design of the particular device you have, nor of your distribution system, so I'm making a few assumptions which may not apply in your situation. Depending on the type of SPD, your device may not even include current surge protection, which makes the analysis much easier. Most reputable SPD manufacturers have very good tech support, so you may be able to call them and get a clearer answer for your specific installation.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Anonymous Poster
#4

Re: Neutral Wire Missing

10/01/2009 2:24 PM

This is this an industrial setting? What are you trying to protect on this system?

Being a voltage of 277Vl-g.... I assume this is an industrial application. Once again they are designed for more sensitive equipemtn. I dont think the SPD will do much but sure go for it. Splce the bond/neutral together as the neutral turns into the groud back at the main service/tx anyways.

Good luck, and remember, turn the power off!!!!! I lost too many friends this way

Register to Reply
Participant

Join Date: Sep 2009
Posts: 3
#5
In reply to #4

Re: Neutral Wire Missing

10/01/2009 9:33 PM

It is a Radio Broadcasting Company. They have transmitter. Actually, they don't have any usage of the 277v. Just the 470v.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); kwoznia1 (1); pwr2thepeople (1); rossmmac (2)

Previous in Forum: Request calculation design for Rectiformer   Next in Forum: Dry-Type Transformers

Advertisement