Thermocouple Life Span

10/01/2009 12:57 PM

I need to know the life span of a thermocouple. The reason I am asking this is I am changing thermocouples after about three months. They break or just don't read properly. I am measuring glass at around 1300 deg. C using type B

__________________
LUCK: A prepared man meets opportunity
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#1

Re: Thermocouple life span

10/01/2009 1:07 PM

You can go up to about 1800 C with a type B. Are you using a thermowell? You should be.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Thermocouple life span

10/01/2009 2:27 PM

That doesn't sound right as thermocouples used correctly generally don't fail. Are you sure they are not suffering mechanical damage?

Are the thermocouples being subjected to vibration, bending or excessive handling?

If so then you need to either support them better or try a different type of temperature sensor such as an encapsulated or sleeved thermocouple, etc. The right sensor for the right application.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Dec 2006
Location: Germany 49° 26' N, 7° 46' O
Posts: 1950
Good Answers: 109
#3

Re: Thermocouple Life Span

10/02/2009 3:23 AM

Glass is very corrosive at these temperatures so you should use the correct tubing - I would try aluminum-nitride.

Any metal (including platinum) will go into solution either as oxide or as nanodispersed metallic clusters of a few 100 to 10000 atoms per cluster or as solid solution of metals in glass.

RHABE

Register to Reply
Guru
United Kingdom - Member - Hearts of Oak Popular Science - Paleontology - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2005
Location: In the Garden
Posts: 3389
Good Answers: 75
#4

Re: Thermocouple Life Span

10/02/2009 4:07 AM

Talk to your thermocouple supplier...either their products aren't performing as they should, or you're using the wrong product for that application. They will be able to advise.

Then contact a couple of other suppliers and check the answers

I have used:

TC-Direct: their K-type t/c lasted for 3 - 4 years underneath buses (we fitted them as a stop gap!)

Watlow: High tech automotive grade t/c used in our production products.

You don't say where you are, so there's a UK and a US supplier there.

Good luck

__________________
Chaos always wins because it's better organised.
Register to Reply
Power-User
Hobbies - CNC - New Member Hobbies - Musician - New Member

Join Date: Jan 2007
Location: South Africa Johannesburg
Posts: 187
Good Answers: 3
#5

Re: Thermocouple Life Span

10/02/2009 4:24 AM

Type B: Platinum-Rhodium(30%) At 1000 deg C 9uV/deg C change

Continuous use +100 to +1600 deg C

Short term +50 to +1750 deg C

BS4937 part 7, ANSI/MC96.1 type B, DIN IEC B8, NF C42-321, JISC 1602

It would certainally apeare you are using the right type of thermocouple. The problem may be elseware as others have suggested. A higher rating type would be W (Tungsten) Up to +2600 deg C The change in voltage would be 20uV/deg C @ 1000 Deg C

Ive being using type K in a heat exchanger at 360 deg C for 10 years, no problim yet.

__________________
Think and move like an electron
Register to Reply
Anonymous Poster
#6

Re: Thermocouple Life Span

10/02/2009 8:20 AM

Many manufactures make TCs to withstand the temperature that you are working at... (cutting costs)... We had TC type K... that where lasting 6 to 12 months....

We then changed suppliers.. now using Endress Hauser ... Our TCs have been in service for 3 years running working with a temperature of 950ºC 24 hrs per day 365 days a year.

Register to Reply
Power-User

Join Date: Mar 2008
Location: MA 01864, USA
Posts: 453
Good Answers: 7
#7

Re: Thermocouple Life Span

10/02/2009 8:32 AM

I have used for more than 25 years thermocouple in glass processing and melting. You need to know glass chemistry if your thermocouple is expoused to the glass vapor.

The life goes to more than 5 years since I have one which has not moved a 1C in 5.3 years if you can take care of protecting your thermocouple tip from glass vapor and furnace contamiantion.

If you need further help I can send you drawing and design how to do that

__________________
Masyood
Register to Reply
Member

Join Date: Sep 2009
Posts: 6
#8
In reply to #7

Re: Thermocouple Life Span

10/03/2009 6:04 AM

Got some insight there guys. Masyood, I will be very gratefull if you can provide me with the drawings.

__________________
LUCK: A prepared man meets opportunity
Register to Reply
Power-User

Join Date: Mar 2008
Location: MA 01864, USA
Posts: 453
Good Answers: 7
#9
In reply to #8

Re: Thermocouple Life Span

10/03/2009 7:50 AM

If I have email will do that. I do not think you need this type of information in public domain.

you can always send email since I have business and may take few days to send that

__________________
Masyood
Register to Reply
Guru
Hobbies - Musician - Tube Amps Only Please!

Join Date: Apr 2009
Location: Los Angeles, California USA
Posts: 553
Good Answers: 1
#10

Re: Thermocouple Life Span

10/20/2009 11:57 PM

It should be in the manufacturer spec or call them up.

__________________
Regards, Maveric Manic - 'Knowledge is Power and Wisdom is knowing how to use it'