Compressed Air Required For Fire Sprinkler System Application?

10/01/2009 2:37 PM

I am working on a Fire Protection Sprinkler System project, which requires 475 GPM of water for 60 minutes at 60 PSIG stored in a 28,000 gallon receiver, and hold 60 PSIG for 60 minutes. Can someone help me with the formula to calculate how much compressed air will be required for this application. Your assistance is greatly appreciated.

__________________
Real Peace is not only the absence of conflict, but also the presence of justice.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2008
Location: Sebring, Florida
Posts: 923
Good Answers: 25
#1

Re: Compressed Air Required For Fire Sprinkler System Application?

10/02/2009 1:04 AM

I would suspect that you would have an electronically controlled valve preventing the water from entering the system until the demand becomes necessary, ie: a fire melts the little fuse link at the sprinkler head where the action is. This is called a dry system and is required where freeze conditions exist. Some compressed air/nitrogen must exist in the line to prevent tripping the electronic signal, that is what alerts the solenoids to act, opening the main valve that permits the water to enter the pipeline. It is not a great deal of pressure or you would have a real maintenance problem with the sprinkler heads.

TMF

__________________
The only problem with common sense, is that not very many people have it, or know how or when to use it.
Register to Reply
Commentator

Join Date: Jun 2009
Location: Between India & Australia
Posts: 71
Good Answers: 3
#2

Re: Compressed Air Required For Fire Sprinkler System Application?

10/02/2009 3:20 AM

Pls specify why you need compressed air. If it is just for the sprinkler pipe to keep it dry and pressurised, you only want a makeup - which is not major. I think there is some mention of the air makeup required in NFPA13/850.

__________________
Continuous Learning
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#3

Re: Compressed Air Required For Fire Sprinkler System Application?

10/02/2009 5:48 AM

Question: is it the air as a fail safe pump?

In this case it depends on the maximal pressure you can generate.

The time is long so that you can consider an isothermal pressure reduction and you can write that the volume at high pressure is equal to the volume at low pressure multiplied by the pressures ration. Up to you to choose which way you accumulate the air. Of course a safety coefficient of at least 1.25 should be considered since over long time periods leaks can occur. The best would be to have a small compressor and fill automatically the high pressure reservoir if pressure drops under a safe threshold.

Between high and low pressure you should have a valve limiting the low pressure to the level you want to maintain it.

Register to Reply
Commentator

Join Date: Jul 2008
Posts: 97
Good Answers: 2
#4

Re: Compressed Air Required For Fire Sprinkler System Application?

10/02/2009 7:40 AM

Multiply the 475 Gals/Min x 60 Min to get the volume of water you need to replace with air, convert it to cubic feet and convert it to SCF. As long as your air receiver pressure does not drop below 60 PSIG plus line losses to water tank with this Std Cubic Feet of volume removed you are okay.

Note, at a previous company I worked at we used a similar system for Fire Suppression in a Hyperbaric Chamber.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: Compressed Air Required For Fire Sprinkler System Application?

10/02/2009 2:37 PM

One gallon(US) is .13386 cubit foot of volume. So 475 gpm of water is 63.498 cfm of water.

I would rate the compressor about 20% larger in cfm.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Anonymous Poster
#6

Re: Compressed Air Required For Fire Sprinkler System Application?

10/04/2009 6:36 PM

Check with the licensed qualified individual with your company.He/she is qualified to make the calculations required.If you or your company are not licensed, you are breaking the law and are putting lives and structures at risk.

Register to Reply