Phase to phase fault

10/03/2009 11:27 PM

We are trying to make a report for a possible phase to phase fault for an electrical distribution system to a two (2) residential blocks with (2) different source of supply.

During troubleshooting the fault was trace coming from one car park lamp pole A wherein the said lamp pole A was supplied by two (2) different source supply. This condition was happened because of the reported lamp pole A was no light. To make the story short the electrician isolate the lamp pole A and take the supply from other source since they want to rectify the problem immediately or temporary.

Now the question is how come that the two residential blocks incoming supply trip one after the other, since the electrical supply for both blocks are equiped with protection?

Anybody who can advise or help me to evaluate this phenomenom.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Phase to phase fault

10/04/2009 11:55 AM

I don't quite follow your text in explaining what actually happened. My best suggestion for you though is to lay out a circuit diagram of the mis-wired configuration with two separate voltage sources and apply some fundamental network analysis. Likely this will not reveal an immediate answer, for you implied that lamp worked for awhile. Now you should add the observed failure phenomena.

But now that I've started to type an idea comes to me. Consider the possibility that the lamp was wired hot to hot of two different voltage source phases that on the day of the repair happened to have the correct phase angle that the electrician measured a hot to hot RMS voltage difference that was identical to the expected hot to neutral voltage he thought he was wiring. Since the two sources are not synchronized to each other, the phase between your two sources will drift. The voltage across the lamp would vary accordingly with this drift to levels that will exceed the lamp's rating.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Participant

Join Date: Oct 2009
Posts: 3
#2

Re: Phase to phase fault

10/04/2009 11:28 PM

If both circuits are using typical breakers, they have what could be considered solenoids built into each one. When the short occurs, there is a rapid inrush which triggers the internal mechanism, and opens the circuit. Sometimes only one breaker will trip. Sometimes aging changes the characteristics and its reaction varies.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: Phase to phase fault

10/05/2009 12:20 PM

The one time I saw a similar occurrence, both incoming supplies were equipped with differential protection. A differential relay sums all currents into and out of the breaker. In normal operation, the sum at any given instant should be zero. The differential relay will trip the breaker if the sum is other than zero. For example, a US Ground Fault Current Interrupter (GFCI) looks at current in the hot & neutral conductors, and will trip if the error exceeds 6 mA.

In my case (and possibly yours), the current to the improperly wired device left source 1, but returned to source 2. The utility would simply see unbalanced load, which is a common occurrence. The differential relay on each source would see a non-zero sum equal to the current drawn by the lamp and would trip.

In order to verify the actual cause, it would be helpful to know the type of protection for both supplies. Are they circuit breakers or fuses? If circuit breakers, what type of tripping is used? Is it overcurrent only, or does the breaker have a shunt trip with a programmable protection device? A one-line distribution diagram for both blocks, including the first utility connection point, would also be useful.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Participant

Join Date: Oct 2009
Posts: 4
#4

Re: Phase to phase fault

10/06/2009 4:21 PM

The problem seems to be the pole. Why will the lamp not burn?Any individual Breaker provided for the lamp pole? How has the Electrician Isolated the Lamp Pole? A single line diagram will give a better clarity to the problem.

The supply to the residential supply will trip if the relays are not set properly or if the downstream breaker closest to the lamp pole does not trip hence the question why will the lamp not burn?

Register to Reply
Active Contributor

Join Date: Dec 2008
Posts: 19
Good Answers: 2
#5

Re: Phase to phase fault

10/07/2009 9:02 AM

I believe that there is insufficient information to make an educated decission regarding the cause of your problem. I also believe that if you are unable to supply sufficient information regarding the installation to allow a report to be made, then you will never understand the problem sufficiently to supply an accurate report.

There are many factors to consider and tests which should be done by some competent person:

What do you mean by a Phase to Phase fault? I can only assume that you mean the phase from one source of supply to the phase of the second source of supply, which may or may not be the same phase at the origin of the supplies.

The practice of using two different sources of supply for one circuit, or even on one set of controls, can be dangerous in itself, unles the load has some sort of identification advising any person working on that circuit, that it has two sources of supply connected, so that any person will not inadvertantly come into contact with a supply that they did not know they should have isolated.

Was the intial supply to the lamp completely and correctly isolated prior to the connection of a second supply?

A test should possibly be made of the Insulation resistance of both supplies as well as between both supplies, as there should be no electrical connection between the conductors of either supply or between the two supplies when isolated or connected to the load (Light). An Insulation Tester should be used for this test. The type and testing voltage being dependent upon the applied voltage of the system.

The type of protection used on the system?

If an RCD is used for protection, along with any other type of protection, then was the Neutral conductor also completely and correctly isolated. If not then you will continue to have problems with the RCDs tripping.

A neutral from another circuit can also lead to unsafe conditions in the supposedly isolated circuit. An incorrectly connected Neutral conductor is as dangerous as an Active conductor and can easily cause a fatal electrical shock.

There are other problems that can also occur with "mixing up" circuits that should never be allowed to occur, but a good knowledge of wiring methods and local wiring rules should prevent this from occurring.

The methods use in the installation will also alter the possibility of different faults occuring, as will the method or type of earthing system used.

I am writing from Australia where we use what is known as the M.E.N System of earthing. I know from many instances of finding wrongly connected circuits that if the earthing system is incorrectly connected, then it is possible this can also cause a fatal electric shock.

My reply may be of little help to you, but I am trying to point out that the problem may be very simple or quite complex, but would certainly need more complete and accurate information for any one to supply you with a satisfactory answer

Regards

Bill Pilgrim

Queensland, Australia

Register to Reply
Register to Reply 5 comments