Power factor with VFD's

10/03/2009 6:26 PM

Do you folks believe that VFD's increase power factor on generators? Knowing that true rms readings should reveal the answer to my question but there seems to be some contirversy arise. For example, world classed yachts use an abundance of VFD's for HVAC resulting in harmonics. None the less, my readings with true rms instrumentation have reduced the pf to around a 0.96! What am I not seeing? Reason, overload setting for short time pickup in generator breaker settings.Thanks for any input.

Jim

__________________
Thank you for your help - By far the best info site!
Register to Reply
Pathfinder Tags: electrical engineering
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Power factor with VFD's

10/04/2009 9:32 PM

There are two "kinds" of power factor; 1) Displacemnt Power Factor and 2) Distortion Power Factor. Most PF meters only read Displacement PF, and from a tarriff and penalty standpoint, that's all that counts. So VFDs do appear to improve PF in an AC motor, because the motor's actual PF is essentially filtered by the conversion done by the VFD. But that self same conversion creates harmonics, which itself presents a complex power factor scenario to the line source, referred to as Distortion Power Factor, but this complexity actually interferes with recording instruments in such as way as to not show up. It does, however, still represent the same power delivery issues that Displacement Power Factor does; the source, in the case of your yacht the on-board generator, must still supply all of the apparent power. But the distortion PF varies by the amount of THD, so it's difficult to quantify. The best method of mitigating it is to add line reactors and/or DC bus chokes on each VFD.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#3
In reply to #1

Re: Power factor with VFD's

10/04/2009 10:44 PM

Thanks for your response! Would the smoke then clear if currents were read and then calculated with a simple equation?

__________________
Thank you for your help - By far the best info site!
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#4
In reply to #1

Re: Power factor with VFD's

10/05/2009 8:11 AM

I'm seeing similar things whilst measuring power consumed by new LED T8 replacement lamps. When measureing power with a typical power meter everything looks wonderful. Except that the PF seems to vary quite a bit. Looking at the phase shift with a scope and a shunt resistor makes the problem clear: the noise on the line from the switching power supply is causing spurious readings. Anything that creates harmonics is going to fool a power meter.

__________________
Eric
Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#2

Re: Power factor with VFD's

10/04/2009 10:35 PM

Modern VSDs are big switched mode power supplies, so the load they present looks (after filtering) resistive.

This means much of the wisdom about power factor, noise and harmonics is out of date. Just look at the difference in size and weight of the supply side filters to see how much things have changed..

Look up drive manufacturers sites for a better explanation.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".