10/03/2009 5:25 PM

hi all

is there different between normal three phase motor which every electrician know it and that three phase motor which operated using VFD?

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#1

Re: vfd motor

10/03/2009 6:32 PM

Yes and no! I've been proven wrong with an application with a 5 kV motor as to what I learned in a seminar. However, I believe there is a difference. Winding temperature that VFD motors account for insofar as longevity is concerned. I think that VFD cable should be used to afford for high frequency voltages. It is my opinion that you shoud apply a motor/cable to the application and in the case of VFD's, read the instructions. Some people are full of crap (or out of money), do it right the first time!

__________________
Thank you for your help - By far the best info site!
Reply
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#2

Re: vfd motor

10/03/2009 8:58 PM

The harmonics that VFD's inject can degrade some dielectrics(insulation) and increase heating loss in windings and motor iron. Motors NOT rated for VFD operation may run hotter than normal and the insulation may break down prematurely. There is no way to predict IF or WHEN this will happen.

If a standard motor was over-built and conservatively rated, it could run fine off a VFD. It is also possible that a VFD could damage a lesser built motor in a fairly short time.

Motors RATED for VFD operation have been specifically designed to handle VFD harmonics and should provide the most reliable long term operation.

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: vfd motor

10/03/2009 10:56 PM

Good information can be found here:

http://cr4.globalspec.com/thread/40051

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: vfd motor

10/07/2009 11:33 AM

As you know any VFD supplies fast transients (pulses) only to the motor. These fast dv/dt pulses impose a huge voltage stress on the motor winding insulation. So, many normal motors may not be insulated to withstand this kind of stress. An inverter duty motor has a special carona resistant insulation to withstand these pulses.

Reply
Anonymous Poster
#5

Re: vfd motor

10/07/2009 3:25 PM

Besides you have to consider that certain VFD can produce Common mode currents thats flows trough the bearings damaging it. You can solve this using ceramic bearinngs, non conductive grease, special feeding cable etc.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: vfd motor

10/08/2009 6:09 AM

Ya! Pal! That could be another problem! Thanks for the input.

Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#7

Re: vfd motor

10/08/2009 10:24 AM

High VFD switching frequencies do increase core losses. Main problem though is the ability to drive motor at lower than rated speed at not derated currents but dramaticaly decreased fan cooling capacity. That's the more common cause of failure in normal motors if this factor is not taken into account

__________________
Life is complex. It has a real part and an imaginary part.