Thunder, Lightning and LT ACB Trip

10/04/2009 7:59 PM

Hi All,

Lately i hv encounted a problems which during heavy thunder lightning with storm caused some of my LT (415V phase 50Hz) 4000 AMP ACB tripped and also caused some of the in operating air compressors and blowers trip.We have many LT main switch boards and air compressors and blowers as install at various location of factory.

What is the possible caused ? our earth chamber and impedance are in good condition

Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: Thunder lightning caused LT ACB trip

10/04/2009 8:53 PM

Your earth chamber and impedance is in good condition is another story. What about your factory roof lighting earthing chamber?

Do your factory had a lighting strike earthing chamber and where, which location do you earth your factory lighting strike earth chamber?.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#2

Re: Thunder, Lightning and LT ACB Trip

10/05/2009 11:58 PM

Without knowing a lot more details, it sounds to me as though your circuit breakers did exactly what they were intended to do!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Participant

Join Date: Oct 2009
Posts: 4
#3

Re: Thunder, Lightning and LT ACB Trip

10/06/2009 4:35 PM

Check the lightning protection system installed in the factory. Adding a Voltage Surge Divertor to the incomer of the Main LT Panel will make a difference

Register to Reply
Member

Join Date: Oct 2009
Posts: 5
#4

Re: Thunder, Lightning and LT ACB Trip

10/07/2009 6:16 AM

Eventhough your earthing and impedance are good,but you need to check the bonding among those grounding chamber.

The cause of the promblem are from "Different Voltage Potential"between grounding point.

You need to make sure that all the earthing chamber are bonding together by the ground wire that are buried under ground.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Thunder, Lightning and LT ACB Trip

10/07/2009 11:26 AM

On what fault the LV ACB tripped? If you have a micro-processor based protection release in the ACB, there might be a possibility of earth fault trip. Pl. confirm.

Register to Reply