about motors

10/06/2009 9:00 AM

hi this is imran from pakistan

i have a motor 3 phase 220v can i use this motor directly to 3phase 380v or not

either i use any protection to this motor,any converter or starters.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: about motors

10/06/2009 9:07 AM

You must use a 380:220, 3 phase transformer. You cannot connect it directly to the 380 volt line.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#2

Re: about motors

10/06/2009 2:09 PM

A transformer should work fine if frequency is the same. A transformer may be more expensive than a variable frequency drive (VFD). Check availability and pricing in your area. The VFD will allow precise control of the frequency, voltage, and current fed to your motor.

Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3

Re: about motors

10/06/2009 2:18 PM

If only - by chance - the motor has 6 leads in its box and its windings are connected in delta, then you can reconnect them into star and use the motor in a 380V supply (if also frequency of the motor and the supply coincide).

Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#4

Re: about motors

10/06/2009 4:06 PM

guest; look in the terminal box on the motor where the wires enter, are there 6 brass screws? if so you should be able to reconnect for 380 volts, it may have wires instead, they are usually numbered or lettered, 9 or 12 wires coming out of the motor would be reconnectable for different voltage, this way you will not burn out your 220 volt motor.

perry

Reply
Active Contributor

Join Date: Dec 2008
Posts: 19
Good Answers: 2
#7
In reply to #4

Re: about motors

10/07/2009 10:02 AM

I believe this man has got it right. I worked with a number of motors over many years, working as an electrician in industry and have always found that unless you are overloading the motor severely, that it is possible to reconnect in either star or delta configuration to alter the current. Of courrse you will alter the torque and output power as well. As he has said, you need to look at the internal connections. If you can find an electrician to check, you may find any number of leads terminated in the connection box, but it is not normally a job that a person without experience should attempt with any guarantee of success. I am in Australia and I had the job of connecting a Hydraulic pump and motor that came from the USA. It had 9 leads and I was able to connect it in a combined star and delta configuration to run the machinary successfully. Most motors will tollerate a full 10% overvoltage. Might run a little hot, but then the life would depend on the insulation rating

Reply
Active Contributor

Join Date: Jul 2009
Posts: 17
#5

Re: about motors

10/06/2009 9:58 PM

No the motor will burn out generally 10 % overvoltage is maximum. Check to see if motor is connected Delta or Wye and consult with manufacturer if higher voltage is possible by reconnection.

Reply
Anonymous Poster
#6

Re: about motors

10/06/2009 10:23 PM

no u cant use

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: about motors

10/07/2009 10:59 AM

What is the insulation of the motor? If it is for 220V, then you cannot connect it directly to 380V. It will kill the motor in no time.

Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#9

Re: about motors

10/08/2009 8:42 AM

Check the motor plate. If you see a triangle near "220V" printing AND you have access to SIX connection points in cable box then yes you can (changing to star connection) Depending on it's power range you may also need a starter cirquitry

__________________
Life is complex. It has a real part and an imaginary part.
Reply