Anonymous Poster

electrical

10/10/2009 6:14 AM

what is derating of electrical equipment?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: electrical

10/10/2009 7:38 AM

An electrical equipment is designed for a certain rating - may be Voltage rating or current rating - based on use at certain standard operating conditions. But, it may not be practicable to achieve all the standard opearting conditions, at the place & time of its use. So, the equipment is given a new rating based on the actual site conditions. This new rating is normally specified as a factor of the actual rating which is called the Rating Factor. While most of the time it is De-rating factor, equipment can also have an uprating factor, based on the site conditions.

Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: electrical

10/10/2009 8:46 AM

De-rating is often done to ensure that the equipment can perform well and will last a long time. For example...

If I needed to regulate 15V down to 12V with 2A of current I would not use a regulator rated for a maximum input of 15V and a maximum load current of 2A. I would typically use a regulator that is rated for 20V input and 3A out. In that instance my regulator input voltage would be 75% of the maximum or 25% derated and my load current would be 66% of the maximum or 33% derated. The same principle applies to all types of equipment and mechanical designs. The brakes on your car, roof loading bridge loading, electrical equipment in cars.

Without derating we would see a lot more feild failures.

Reply
Anonymous Poster
#3
In reply to #2

Re: electrical

10/10/2009 9:16 AM

Sorry you are wrong and #1 is right.

You are talking about factor of safety, not derating.

Derating is as #1 said- changing the rating as per the actual condition.

Eg a motor is taken up to the top of Mt Everest - there the cooling, and other parameters will burn the motor of say 10HP if the rated load is applied on it.

So the motor is de-rated accordingly (ie it is treated as a lower HP Motor)

De-rating equipment for use at elevations above sea-level. Industrial controls require de-rating when operated at an altitude above 6600 ft. Industrial power semiconductors require de-rating when operated above 3300 ft. The equipment must be derated 1% for every 330 ft above these heights.

Then you may have compensations for RAD (relative air density), Humidity.

The compensations are usually covered under standards (eg NEMA MG1-14.04) and in quite a few cases the manufacturer put added conditions

Reply