Hello
I have
problem with Stamford Generator Type:A07D786842, maker: Cummins generator
technologies Norway AS.
During normal
operation Voltage on this generator suddenly rising up from 440 V to aprox. 620
V, frequency is the same what was before problem is 60 Hz. Voltage regulator
type is Stamford MX 321 AVR
We start
test procedure of voltage regulator as per manual instruction
Cable connections on AVR and on generators was checked
and found everything in order. Also we checked resistance and voltage between
terminals on AVR and we found as follows:
Resistance
between P2, P3, P4 terminals:
P2 – P3 3.07 Ohm
P3 – P4 3.05 Ohm
P2 – P4 3.02 Ohm
Voltage
between this terminals:
P2-P3 201 V
P3-P4 202 V
P2-P4 202 V
And according to manual instruction should be 200
to 216 VAC and this is in range.
Exciter
stator resistance, between terminals:
X – XX 19.45 Ohm - according instructions should
be in range 18 – 30 Ohm and this is OK.
Resistance and
voltage between6, 7, 8 terminals on AVR:
6 – 7 9.08 Ohm and 0.9 to 1.2 VAC this is
not correct.
6 – 8 105 Ohm and 320 VAC this is not
correct.
8 – 7 96 Ohm and 320 VAC this is not
correct.
According
instruction should be 170 to 250 VAC
We
disconnected the cables between Isolating transformer and AVR and the same
value of resistance is directly on transformer terminals.
Resistance
between the others terminals:
E0 –
E1 96 Ohm
K2 –
K1 180 M Ohm
I think that
isolating transformer is out off order but I'm not sure for 100%, Could You
help me solve this problem?
Thanks in
advance
XWS2