how can i calculate the requirement of kvar of particular load?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#1

Re: question

10/13/2009 6:35 PM

Please ask a question with enough information to be answered.

Its like asking, "how do I calculate the moon?". Well, what do you want to calculate? the weight of the moon? the speed of rotation? the amount of gamma rays reflecting from it's surface? how many little men are on the dark side? is it made of cheese? what kind of cheese... alright I'm kind of wandering off topic here....

Please elaborate on your question.

__________________
Don't believe everything you read on the Internet!
Reply
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#2

Re: question

10/13/2009 7:47 PM

Hopefully this can help you find an answer to your question...

http://en.wikipedia.org/wiki/Volt-amperes_reactive

Reply
Anonymous Poster
#3

Re: question

10/21/2009 4:02 AM

I assume that you want to calculate the kVAR of the capacitor required to correct the existing low power factor of a load to a desired target power factor. Right? If so, the capacitor kVAR required for improving the existing power factor (PF1) of a load to a target power factor (PF2) is;

kVAR (C) = kW [Tan (phi 1) - Tan (phi 2)]

where,

kVAR (C) = Capacitor kVAR required

kW = Active Power Rating of the Load(s) connected

phi 1 = angle of existinng Power Factor = Cos-1 (PF1)

phi 2 = angle of target power factor = Cos-1 (PF2)

Reply