do we need to give supply to single phase electric motor through overload

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jan 2009
Location: Anpara,sonebhadra,UP
Posts: 14
#1

Re: motor

10/14/2009 6:48 AM

Yes,a single phase AC motor should be connect through a O/L relay.There are single phase O/L relays are available in market how ever a three phase relay can be used.Out of three terminals one terminal to be connect for neutral and remaining two terminals to be conect in series (incoming terminal of one phase - Out going of the same phase terminal -again from out going of the phase 1 to incoming og phase-2 and final out going will be from 2nd phase out going terminal). it will protect the motor from O/C and other faults like E/F and S/C etc.

Regards

Binod Kumar Panda

__________________
Binod Kumar Panda
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: motor

10/14/2009 7:13 AM

Depends on your motor size.

BS7671:2001 states that motors over 0.37kW need an overload device.

More recent specs may vary - I don't have the latest edition to hand - and as I don't know where in the world you are, I can't comment on your local regs.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: motor

10/14/2009 11:40 AM

Some small 1 phase motors have a thermal OL device built-in to the motor. If the nameplate says "Internally Protected" or something along those lines, then it has that feature. If not, assume it does not and use an external OL relay. If all you have available is an IEC type 3 phase OL relay, make sure you read the instructions for it regarding looping the wiring back through to ensure that current is flowing through all 3 legs, otherwise it may give you nuisance trips.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**