I have confussed about the size in sselection of the analog signal cable, I am using the 1.5 sqmm size cable if i will use the 0.5 sqmm size cable for same loop then what is the effect on the signal measurement

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: what point consider for selection of the analog signal ( 4-20ma)cable

10/14/2009 2:34 PM

None whatsoever, provided the loop resistance is less than the maximum for the voltage and the transmitter manufacturer's instructions. Provided they have low enough resistance, two bits of wet string would do for circuit conductors.....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: Selecting Analog Cables

10/15/2009 1:45 AM

Hi there,

When sizing a cable there are a few things to bear in mind.

1. Total length of the loop.

2. Instrument impedance, inductance and capacitance.

3. Cable (conductor) impedance, inductance and capacitance.

You then need to look at your local regulation as well as the instrument manual. Here you will find what the maximum percentage volt drop across the loop may be as well as the maximum impedance, inductance and capacitance across the loop may be for the instrument to function.

You can then look at your cable data sheet and calculate these factors very simply from there on. The bigger the conductor size, the less the impedance, inductance and capacitance will be.

Regards,

Craig

Reply
Guru
Hobbies - Musician - Tube Amps Only Please!

Join Date: Apr 2009
Location: Los Angeles, California USA
Posts: 553
Good Answers: 1
#3

Re: Selecting Analog Cables

10/20/2009 11:51 PM

Use double shielded coax or triax for best low noise results.

__________________
Regards, Maveric Manic - 'Knowledge is Power and Wisdom is knowing how to use it'