IDMT Relays

10/14/2009 9:31 PM

AREVA (previously ALSTOM) make IDMT relay - Overcurrent & Earthfault relay contains a PSM Vs Time Multiplier Values on it's name plate.

But some intermediet value of PSM Vs Time Multiplier is missing on it.

Can any one suggest the complete graph and/or intermediet values ?

__________________
Thanks
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#1

Re: IDMT Relays

10/16/2009 12:19 PM

Please see the following formulae Standard inverse charectristic is t = TMS x 0.14 Divided by [ ( M to the power 0.02 )-1 ] Where TMS - Time Multiplier Setting (0.01- 1), M is current mutiple [ arrived by Fault Current for which time to be arrived divided Actual(Effective ) CT ratio] Effective CT ratio can be arrived by Adopted Ct ratio x PSM (Plug Setting Mutiplier adopted in the relay) For example if you have feeder relay connected to a CT Ratio 400/1A with PSM adopted as 50%, the Effective CT Ratio will become 200/1 Suppose the Fault current is 2000 A, for which the time of operation is to be calculated for a TMS of 1,the value of M will arrive as 10 . on subtituting this you will get a time of 2.97 which is approximatly equal to 3. Or other wise above formulae is intended for 10/ 3 Sec graph of IDMT relay For other graphs also similar formulaes are available From the above formulae you can calculate time graph for intermediate current mutiple other than those specifically mentioned in the Relay name plate itself

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2009
Location: Mumbai
Posts: 73
#2
In reply to #1

Re: IDMT Relays

10/17/2009 2:52 PM

Dear Mr. Panner Selvam, many many thanks to provide me such a perfect formula to know the intermediet values of entire range. Sir, just I wanted to know that where u have got this formula? I am really very much thankful to u because from the last 6 moths I am asking this question to no. of expert engineers but unfortunetly they could not provide me any satisfectory aswer.

Sir, Thank U Very Much

__________________
Thanks
Register to Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#3
In reply to #2

Re: IDMT Relays

10/18/2009 3:52 AM

Please refer any protection manual for numerical relays by any reputed relay manufacturers like Areva, ABB, SEL, GE,Etc. All the distance relays or differential relays, or generator protection Relays, are provided with O/L relays as backup protection Schemes. These relays are configured to operate only by using different algorithms for different characteristic Standard Inverse, Very Inverse and Extremely inverse, thermal characteristics etc You can Down load manuals from their Websites. All the best.

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: IDMT Relays

10/20/2009 7:58 AM

This algorithm is derived from the IEC Standards (IEC 60255). It gives the algorithm for various curves such as Normally Inverse 3 sec., Normally Inverse 1.3 sec., Very Inverse and Extremely Inverse.

The formula is:

t(I) = {(A) / [(I/Is)a -1]} x TMS

Where,

t (I) = trip time at the actual current 'I'

A = Constant (varies for different curves)

I = Actual current through the relay

Is = Set current

a = another constant (varies for different curves)

TMS = Time Multiplier Setting

For example for NI 3 Curve, 'A' is 0.1414 & 'a' is 0.02.

Register to Reply
Commentator

Join Date: May 2009
Location: Mumbai
Posts: 73
#5
In reply to #4

Re: IDMT Relays

10/20/2009 1:52 PM

Thank u Mr. electricalexpert65. Can u please tell me where can I get these curves ? How the value of 'A' & 'a' is obtained? pl. explain me in detail with example.

__________________
Thanks
Register to Reply
Anonymous Poster
#6

Re: IDMT Relays

02/12/2011 12:25 AM

"A" and "a" are constants that set the extend of "inversity" of the curve, i.e. how fast the operating time drops as current increase (in actality be it is "how fast the slope of dt/dt drops with an increase in current") . The values of these constants are:

For a normal(i.e. moderate) inverse curve: (A,a) = (0.14,0.02)

For a very inverse curve: (A,a) = (13.5,1)

For an extremely inverse: (A,a) = (80,2)

For a long-time inverse:(A,a) =(120,1)

I think normally they use the Greek letter "beta" instead of A used here, and the Greek letter "alpha" instead of the "a". So I think it would be better to call them (beta,alpha) or (B,a) instead of (A,a).

See http://myweb.tiscali.co.uk/robert.booth/uni/docs/Power%20Supply%20Assignment%203.pdf

Register to Reply
Participant

Join Date: Dec 2012
Posts: 3
#7
In reply to #6

Re: IDMT Relays

12/09/2012 9:38 AM

There is a good explanation on how to calculate the tripping time (both for IEC and IEE) in the link below. The site also has an online calculator which will allow you to work out the tripping time for various curves and settings.

myElectrical - Post on IDMT curves

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BinbinB (1); dhanesh.koshti (2); electricalexpert65 (1); Panneer Selvam (2)

Previous in Forum: Lead Acid Batteries   Next in Forum: Bureau Veritas

Advertisement