Previous in Forum: Diff:-Short Circuit Current 21 for 3sec and 21 for 1Sec   Next in Forum: PLASMA SCREENS
Frequency/voltage connverter
10/17/2009 5:04 AM
Please suggest the best way to convert 230/60HZ 3phase to 415/50HZ three Phase?
We are shifting our plant to saudi arabia, the Load is 3MWatts.
satdan
Good Answers: 804
Re: Frequency/voltage connverter
10/17/2009 11:45 PM
So you have 3MW of load that is running at 230V 3 phase right now, and you want to take that to Suadi Arabia where they have 415V 3 phase, correct?
If so, buy a generator, it will cost you less in the long run.
10/19/2009 1:11 AM
No, My plant is running at 415/3Phase 50HZ, But it is a 2 Year project and it is finsished now. Now the plant is permanently shifting to saudi.
we can use generator as temperory solution, to utilize the Grid power supply, I need best frequency converter.
Thanks for your suggestion
satdan
10/18/2009 2:31 PM
This is a common question on CR4.
Check your loads and see if they will work on 50Hz, if they will then buy a step-up transformer. If you really need 60Hz, buy a generator. If price is a concern, buy a generator for the 60Hz loads and a step-up transformer for the 50Hz loads.