Ultrasonic Flowmeter (FH8300)

10/19/2009 7:13 AM

Hi Guys,

Need your help with regards to the Ultrasonic Flowmeter (FAURE HERMAN FH8300). I'm having problem of the 4 to 20mA output. The instrument is having an output of 8.5mA without flow and on the LCD display show 0m3/h. But on the DCS side show 19.3m3/h suppose to be it's zero.

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Ultrasonic Flowmeter (FH8300)

10/20/2009 1:17 AM

You must to calibrate analogue output

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Ultrasonic Flowmeter (FH8300)

10/20/2009 3:28 AM

Contact the manufacturer for advice. Without seeing the wiring diagram as installed, it is difficult to suggest anything else.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator
Engineering Fields - Control Engineering - New Member United States - Member - New Member Popular Science - Weaponology - New Member

Join Date: Jan 2009
Location: Berkley MA
Posts: 88
#3

Re: Ultrasonic Flowmeter (FH8300)

10/20/2009 7:52 AM

I agree with the previous responder that stated that one must calibrate the analog output but also the DCS input needs to be re-calibrated by some reprogramming of the DCS.

With all ultrasonic flowmeters, one must ensure that the system parameters are entered correctly (fluid parameters like fluid temperature, specific gravity or in some flowmeters the actual liquid being measured, pipe parameters like pipe diameter,pipe material and pipe wall thickness). Incorrect entered pipe parameters can cause incorrect readings due to a phenomenon called beam scattering, in which the sent ultrasonic signal will travel around the outside of the pipe vice through the pipe wall through the fluid and through the other side. Because the flowmeter scales its output power in accordance with the entered pipe and fluid parameters, there is not sufficient emitted power to go through the pipe wall at both ends. To minimize this we used duct tape along the sides of the output transducer, from the back to approximately 4 inches forward in the direction of beam travel (same as flow direction). If the transducers are mounted in reflect mode and the distance is short enough (small diameter pipe), then the tape is mounted along the sides of the transducers from the back of the emitter to the back of the reciever. This method is especially helpful when non-standard pipe wall thicknesses are inuse.

Also check to see that the transducers are mounted correctly, either in direct mode or reflect mode. If there is a small amount of misalignment, this will cause incorrect readings or none at all. Most ultrasonic flow meters come with mounting brackets (Siemens/Controlotron do, I am not familiar with others) that will make it easy to mount and calibrate. Also, ensure there is sufficient coupling compound, either too little or too much can affect the reading.

The above information I have gotten from my own experiences with ultrasonic flowmeters and I am glad to pass this on.

Good luck

__________________
Only two things are infinite, the universe and human stupidity, and I'm not sure about the former.
Reply
Anonymous Poster
#4

Re: Ultrasonic Flowmeter (FH8300)

10/20/2009 9:52 AM

If your calculated calibrated max flow is 36.415 m3/hr, then the DCS side is indicating correctly, and the output from the meter needs to be calibrated for proper zero and span.The LCD display may be malfunctioning if it indicates zero flow with a milliamp input, or input polarity may be reversed.Check connections to input resistor of LCD display for good continuity.

It is advisable to start from the beginning and calibrate all indicators from scratch, using an accurate milliamp source,and finalizing with the meter output itself.This way, all outputs will agree with each other.

Confucious say:Man with two watches never know exactly what time it is.