Gensets and Chiller Compressors

10/21/2009 11:02 AM

I want to connect 120 hp chiller compressor to 250 KVA genset, will it really affect the performance of genset.

Suppose if run the 120 hp chiller compressor through VFD to 250 KVA genst what will be the effect of genset.

Is there standards available for selection of genset to this particular application

Is there any possibility of connecting 120 hp chiller compressor to 250 KVA genset.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: possibility of run the 250kva genset with 120hp chiller compressor

10/21/2009 11:39 AM

A genset needs to be sized to handle all the loads that will be imposed, plus sufficient reserve to be able to start the largest motor. The 120 hp chiller equates to 89.52 kw. Conservatively assuming a power factor of 0.85, this is 105.3 kva. With reduced voltage starting (or soft start or VFD), this looks okay, so long as no other large loads are present when starting the chiller. Once the chiller is running, other loads could then be added.

The chiller control system should also ensure that the chiller starts unloaded, and then loads up after reaching full speed.

Check also with the genset manufacturer. It may be rated as to the largest motor it can start under various types of starting.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
5
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: possibility of run the 250kva genset with 120hp chiller compressor

10/21/2009 5:17 PM

It may be repeated but here it is again.

Question:

What size of Generator is needed for starting an induction Motor?

Answer:

For DOL starting, 4 times the motor capacity

For Soft Starting, 2-3 times the motor capacity

For VFD, 1.4 times the motor capacity

So, in your case 120 HP (89.52 kw) motor through the VFD with 250 KVA (≈ 200 kw) generator should be fine.

Please see the previous thread:

http://cr4.globalspec.com/thread/41125

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: possibility of run the 250kva genset with 120hp chiller compressor

10/21/2009 10:08 PM

Thank you for improving on my earlier answer. I think we are agreed that the OP's application looks good, and I am glad to have this additional information. I would give it 2 GAs if I could.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: possibility of run the 250kva genset with 120hp chiller compressor

10/22/2009 2:35 AM

you need to check the Rating of the genset (Standby/Prime/Continues) if its standby set you need to discuss with genset engine manufacturer, second check Block load characteristics of genset engine manufacturer which will help you better.

crm

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Gensets and Chiller Compressors

10/22/2009 6:00 AM

I would like to know the starter type for this compressor. If it is DOL, then definitely the DG set will sink during starting of this appliance. If reduced voltage starting, may be star-delta or auto-transformer, the DG set might just handle the situation, depends upon the base load on the set at the time of starting the chiller. A VFD would definitely help as all VFDs are soft starters inherently. The DG set will definitely handle the starting of this chiller if the chiller is driven thro a VFD. But a word of caution - check for harmonics from the VFD. It might cause voltage distortion in the DG set.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); msamad (1); Tornado (2)