Capacitor Groups

10/23/2009 5:12 AM

HI

i would like to ask about correction of power factor for an electrical system by using

capacitor groups on 11 kv delta side of an 250 mva auto transformer ,and i like to know the advantages and disadvantages of this plan .

thanks very much

ALI RAOOF

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Capacitor Groups

10/23/2009 5:59 PM

ALI

Are you trying to correct the power factor of the load on the 11 kv side of the transformer or on the primary side of the transformer? Tell me again what the plan is please.

Register to Reply
Participant

Join Date: Oct 2009
Location: IRAQ- KIRKUK
Posts: 3
#4
In reply to #1

Re: Capacitor Groups

10/24/2009 5:00 AM

HI

i have an electricity plan contain of two sides of voltages ,400 k.v grid & 132k.v network , both sides connected together through auto transformers by capacity 250 mva for each one and having 11 k.v coils connected as delta which effect on both sides voltages,sure an auxilliary of power plan and zigzag transformer and earthing resistance and tertiary reactor contain by this low voltage side ,what i need to ask is that i need to choose capacitors groups on 11 k. v side to correct the voltages and mvar for both sides of transformer .thanks

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: Capacitor Groups

10/25/2009 10:57 AM

Please note that the primary reason for the Delta connected tertiary in your 400/132kV, 250MVA auto-transformer is for providing a path for the circulation of zero sequence currents, which otherwise would circulate in the transformer main windings thus causing additional heating. Do not use it for PF correction.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#2

Re: Capacitor Groups

10/24/2009 12:52 AM

what is the type of load, that is:- motors, lights, a combination of the two - and the size of the load in kw?

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#3

Re: Capacitor Groups

10/24/2009 1:38 AM

Please confirm the Voltage ratio of the Auto transformer. It is not advisable to load the Auto transformer Tertiary for PF correction. Even though the it will Correct the PF on in-commer side, it very costly suggestion and it will reduce the out put on secondary side of auto as the capacitor will be construed as a load on the territiary winding. We had very bad experiences when we operated similar connection of 10 mva capacitor on the tertiary delta of 230/110 KV, 100MVA Auto There are successful Schemes of connecting 110 KV/24 MVA Capactor banks on 110 KV Busses of EHV Substations. It is better to adopt such Schemes instead of connecting capacitor to the Teritiary winding of Auto Transformers Good luck

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

aliraoof (1); brich (1); electricalexpert65 (1); Panneer Selvam (1); wareagle (1)