I am using ABB SPAJ140C Over current protection relay for the transformer feeder 630KVA,13.8KV / 220-127V.
The Current drawn at primary is 15 ampere.
The CT ratio is 100 / 5 Amp.
The overcurrent unit of SPCJ 4D29 of ABB SPAJ140C unit; the low set over current stage I > at definite time characteristic is 0.5 --- 5.0 X In ( Where the rated current in my case is 5 Amp ).
To protect the transformer on overcurrent, if it is above 20 Ampere; what setting I have to choose to acivate my protection relay to trip.
0.5 setting belong to 10 Ampere or 50 Ampere ?
1.0 setting belong to 20 Ampere or 100 Ampere ?