what is the effect of missing one phase from feeder , the feeder is parallel with other feeder . both feeding 12mw load , the system is 3 wire system , grounding by zig-zag transformer . each feeder 10 mw , 6.6kv
Re: lossing phase
10/26/2009 6:31 AM
The corresponding phase on the feeder that is still connected to the load will overload above 10MW, thereby causing its circuit protective device to operate and disconnect the overload.
Re: lossing phase
10/27/2009 12:53 AM
Apparently, the load will experince unvalance voltage which may cause the sensing device to trip.
every second counts in our life...
Re: lossing phase
10/31/2009 5:11 PM
it was like this, when the operator switched off the feeder which messed one phase, the breaker opened not completely and one pole stayed closed , that cause the ground transformer and ground resister are burnt , trip other feeder.
is what happend made such high current in the ground (more than 250A) .