CT ratio & burden

10/28/2009 1:28 AM

if i have protection CT with multi CT ratio (1000/500/1) with design Burden 15VA

is this burden same for all the ratio

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: CT ratio & burden

10/29/2009 7:34 PM

I am not too sure as it has never come up (we don't use multi-tap CTs). I was interested myself in knowing the answer but a quick search of the internet produced no clear answer.

If the CT is rated at 15VA burden then it is probably 15VA when connected 1000:1. 500:1 will result in lower secondary winding resistance and therefore allow a theoretically higher burden, but I don't expect the turns ratio to burden relationship to be linear (ie- 500:1 ratio to allow a burden of 30VA).

http://en.wikipedia.org/wiki/Current_transformer

For safety reasons I would assume that 15VA is your burden limit even if you intend to use the lower turns ratio (500:1).

Alternatively you could test the CT or discuss directly with the CT manufacturer.

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: CT ratio & burden

11/01/2009 6:15 AM

Yes! The burden will remain same as long as the secondary current is same.