I am working on an electrical system design to be supplied to Chinese customer. The basic design is by German colleagues. A portion of the design has me concerned.
A power cabinet which provides MCC functionality is fed with a 1600 A feeder (380VAC 3-phase). Ahead of the main breaker, they have tapped wires off to a 400 A branch circuit. Therefore a single incoming feeder effectively feeds a 1600A breaker in parallel with a 400A breaker.
The main feed cable for ~2000 A is brought in with sufficiently sized cable and landed on a copper bus bar which is terminated at the U/V/W terminals of the main 1600A breaker. Those bus bars have smaller (sufficient for 400A) cables routed to a 400 A breaker. The distance is short - 1-1.5m (or less) of cable and within a single cabinet bay.
The fabricator is using a flame-retardant cable they have identified as "Short-circuit-proof" (meaning the insulation will not ignite prior to completely open circuiting and eliminating the fault current).
That length of wire is only protected by the 2000 A CB located a distance away in the plant sub-station.
Can anyone provide any experience in this type of application and possibly point me to some code standard (or more likely an exception granting) which allows this. The colleagues asure me they do it all the time and it is perfectly acceptable - but they can't point me to a code standard indicating so.
"Almost" Good Answers: