Anonymous Poster

Contactor Fails Repeatedly

10/28/2009 6:23 AM

I have a 9kw pumps 380volts 3phase.The contactor is DOL 110vac supply voltage. 1 case one of the pole in contactor is burnt out and i changed a new one, after a month it happen again. What could be the possible cause of this burnt out?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: burnt out....

10/28/2009 7:22 AM

Overcurrent in that particular phase.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#2

Re: burnt out....

10/28/2009 7:55 AM

burnt out; the 110 volts may go lower when pump starts, causing the contactor to chatter. perry

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#3

Re: burnt out....

10/28/2009 8:30 AM

Loose connection somewhere down the line to the pump.
Should change all contacts at same time as well as any mounting hardware or springs if applicable.
Inspect wire condition for good clean connections.

For starters.

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Reply
Commentator

Join Date: Jul 2009
Posts: 63
#4

Re: Contactor Fails Repeatedly

10/28/2009 4:39 PM

May be an idea to check the rating of the contactor,the AC3 rating.

Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#5

Re: Contactor Fails Repeatedly

10/29/2009 7:29 AM

Yes check the contactor rating, also if pump is starting and stopping a lot the rating should be higher than for one which runs continuously

__________________
Dont get on to the roundabout if you dont know how to get off
Reply
Associate

Join Date: Jan 2008
Posts: 34
#6

Re: Contactor Fails Repeatedly

10/29/2009 10:06 AM

It's the same leg all the time, right?

Weak coil, or slight warping in the contactor housing not allowing the contactor points to close all the way on that side.

Reply
Anonymous Poster
#7

Re: Contactor Fails Repeatedly

10/29/2009 12:17 PM

It's likely to be the high (perhaps sutained for a while) start-current of a motor downstream of the contactor.

This happens frequently in high starting-inertia applications such as rock crushing in mines and gravel pits.

At the very least, put in a soft-starter with a long-enough "soft-start" period. We put in an Integra unit manufactured by Somars, which completely solved one of our customers' similar problems. Integra units have soft-start capabilities, but they're much more than soft starters ... they're specialized computers that can be configured to both protect motors and to increase energy efficiency.

http://www.somar.co.uk/energy-saving-technology/Integra-motor-control.php

The starter on a rock crusher kept burning out at weekly intervals, which meant shutting down a crusher, filing (shaving) the starter contacts, and running the crusher for another week. Now, the contactor doesn't burn out any more.

Cheers!
DZ

Reply
Associate

Join Date: Aug 2009
Posts: 33
#8

Re: Contactor Fails Repeatedly

10/30/2009 12:26 AM

The pump is 9KW 380V 3 phase but your DOL starter is 110Vac supply voltage ????Are you sure???How can you start the motor???

Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#9
In reply to #8

Re: Contactor Fails Repeatedly

10/30/2009 1:03 AM

Probably read contactor coil control voltage??

__________________
Dont get on to the roundabout if you dont know how to get off
Reply
Anonymous Poster
#10
In reply to #9

Re: Contactor Fails Repeatedly

10/30/2009 10:40 AM

you are correct. 110Vac is the contactor coil voltage.

Reply
Anonymous Poster
#11

Re: Contactor Fails Repeatedly

10/30/2009 2:42 PM

Possible causes

1) Loose connection

2) Incorrect contactor sizing

3) Incorrect coil voltage (Low Voltage)

4) If there is dirt on the face of the moving metal parts on the contactor. it will chatter... and possibly cause this..

this is also true if the eddy current ring on these metal plates is missing

Reply Score 1 for Good Answer
Anonymous Poster
#12

Re: Contactor Fails Repeatedly

10/30/2009 11:05 PM

Did you check all 3 supply legs to the motor? You may have a dead leg and the other 2 legs are drawing excessive current. edmund

Reply
Anonymous Poster
#13

Re: Contactor Fails Repeatedly

10/31/2009 5:30 AM

For premature failures like that, usual cause is insects: earwigs, spiders, and such. Assuming open contactors, mind you. If open, try to replace with enclosed contactors unit.

Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#14

Re: Contactor Fails Repeatedly

01/28/2010 1:59 AM

Dear Guest,

I have one small request to you. whenever you are asking a question and you want a correct engineering solution. please give a detailed specification of your system.

1) what is the motor application ?

2) What are the environmental conditions? whether explosive like oil refinaries or chemical factory or normal conditions.

3) overload duty cycle of motor.

4) switching operations

if you could give a detailed picture, then the forum can decide whether the starter ratings you have selected for motor is correct or incorrect. Also whether you have incorporated OLR for overload protection.

Thanks and Regards

Reply
Anonymous Poster
#15

Re: Contactor Fails Repeatedly

02/19/2010 11:02 PM

Check for circuit breakers (as said above) "down the line." The failure you are seeing often results from breaking (or, just as typically) from fusing of the breakers...from corrosion or surge such as lightening nearby. These are sometimes out of sight like on the bottom of the panel. For three phase there could be more than one breaker/safety-cuttoff devise. If the reset buttons do not push in readily, that breaker is likely fused/damaged and needs replacement. Overcurrent damage resulting from failed operation of damage prevention device.

Reply
Reply to Forum Thread 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

_Leon_ (1); Anonymous Poster (6); charsley99 (1); Dave M. (1); garth (2); kumarr68 (1); perry (1); PWSlack (1); shanbhag (1)