10/31/2009 4:11 AM

i recently changeg a motor on a decanter machine, the new motor is a cmg motor the motor is rated 380/690 and i am running the motor in star delta. because the voltage for star is 690 my starting current is extremely high the supplier of the motor says this is normal 'note' i never had this problem with the old motor . to solve the problem i moved the over load to the delta contactor and reduced my star time, but this is not good for the machine the motor is like almost starting dol and at almost foll speed . any help on this problem

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#1

Re: problem with motor

10/31/2009 12:33 PM

I need further info ,, is the new motor voltage is the same with the old one ? check that the frequency of new one you're using is equal to the electrical supply frequency .also give us the electrical power (K Watt) of the new one in order to decide if the starting current is normal or not .... initially my advice that when you have to replace a motor owing to any reason , then you use a motor with the same specification of the taken-away motor ....

__________________
Just live and .. Learn!!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: problem with motor

10/31/2009 2:52 PM

The voltages you mention are unfamiliar to me. In star the windings should receive 1/√3 (~0.577) times the line (delta) voltage. 380/690 (~0.551) looks a bit off. I would recheck the wiring closely. Though not likely, it is conceivable that the contactors have been switched, which would start the motor in delta, giving the high inrush current.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3

Re: problem with motor

10/31/2009 2:55 PM

Surprised to hear about a 380/690V induction delta/star motor, I only seen 380/660V ones.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: problem with motor

11/01/2009 6:52 AM

Is the motor meant to run as a dekta-connected motor at 690V? DOL starting in Delta may give you an inrush of say 6X In. If so, in star mode while starting, it should take 2XIn only normally. What is it drawing? Much higher? Then something is wrong. It may take 2Xin for almost 90% of the starting time. Is this worrying you?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#5

Re: problem with motor

11/02/2009 4:45 AM

You don't say how big the motor is but going on some of the happenings around our plant this is what could be happening. Some of the smaller motors turning up at our plant are 3 phase 240V delta connection ONLY or 3 phase 415V star connection ONLY. By conecting it up to a star delta starter you may be wrong voltage to the windings. Please check the name place for this condition. It is particularly easy to miss if the original motor was 415V delta connected. Good luck.

__________________
I attend work so my dogs can have the good life.
Register to Reply
Participant

Join Date: Oct 2009
Posts: 3
#6

Re: problem with motor

11/02/2009 6:32 AM

sorry for not giving all the required information ,i will now try and list all the necessary information. my main problem is that the company that supplied the motor says that even though the motor has two voltages on the name plate, it is still designed to run star /delta . my plant power supply is 380 v 3 phase , i believe that because this motor has a higer voltage rating for star 660v .... i believe this is why i am having problems starting up in star or are they right ?????

1) original motor 25 hp ' new motor 22 kw '

2) start delta starter was originaly overated so there was no need to change

3)no name plate on original motor i got the hp from the user manual

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: problem with motor

11/02/2009 7:06 AM

i believe that the motor will deliver the rated HP when connected in Delta mode on 380V supply or in Star mode when connected on a 660V supply, this being 1.732 X 380V.

You are right in using a star-delta starting method, but you must supply ONLY 380V. So, when in star mode, it will draw 2XIn at inrush, and when it changes over to delta, it will draw In having accelerated and built up the back emf. It will also now deliver the rated power (22HP?)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#8

Re: problem with motor

11/02/2009 11:32 AM

Put it on a VFD

and forget about it.

Register to Reply
Anonymous Poster
#9

Re: problem with motor

11/03/2009 3:20 PM

I guess you just switch the motor on directly without any starting device. Normal three phase motor when suddenly supplied with energy could consume up to 15 times higher current than its max operating current. That calls for installation that could withstand such a huge current surges. Therefore many methods of starting up motors have been develop and the best is to install frequency inverter that that allows keeping current within that of max allowed so saves energy if frequent strating/stopping.

Te supplier is right. This is normal, but expensive to run.

Stan