Detecting Medium or High Voltage Inside an Electrical Panel

11/02/2009 6:42 AM

Hello to everybody. I searched quite a lot inside CR4 before posting my question, but didn't find anything relative. So i am posting my question apologizing on account, in case somebody else had done it before. Question: Does anybody knows if there is an instrument or a device that gives you the opportunity to check the existence of Medium or High voltage inside an industrial electric panel? I am looking for something like a very good insulated "tester", so as to be double protected and secured when working on such panels. And that because sometimes either the measurement instruments on these panels don't work properly or they are not installed at all. I would appreciate any information given (links to commercial or other sites about these kind of instruments/devices etc.) Thank you very much in advance! Keep up the good work! Charalampos

__________________
Charalampos K.Kalothetos - Dipl. Electrical Engineer & Computer Engineer - Polytechnic School of A.U.TH.
Register to Reply
Pathfinder Tags: Device
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Medium & High Voltage existence check device

11/02/2009 6:52 AM

<...Medium or High voltage...>

Please quantify. 'Low voltage' is anything below 1000V. A wide range of equipment is available.

What procedures are in place to prevent personnel from coming into contact with these voltages?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Apr 2008
Location: Thessaloniki - Greece
Posts: 4
#2
In reply to #1

Re: Medium & High Voltage existence check device

11/02/2009 8:11 AM

Hello again. Its quite right to request quantification. When i am talking about Medium Voltage, i am reffering to voltages higher than 1.000V and specifically voltages from 6kV to 21kV (reference to Greece and Balkans Power Electric Grids). Voltages Lower than 1.000V are considered to be Low Voltages. For measuring Low Voltage Loads we use instruments that have an insulation category CAT III-1000V and CAT IV-600V and the equipment we mostly use and you also send me in this link, its satisfactory. Sometimes though we must do some works and measure in Medium Voltage Panels. So i am asking if there is any equipment to prevent personnel from coming into contact with Medium Voltage (higher than 1.000V) and specifically with voltages between 6kV and 21kV. I hope to have answered your question and brigded the gap came up from mine! Hoping to some extra help for finding such equipment. Charalampos

__________________
Charalampos K.Kalothetos - Dipl. Electrical Engineer & Computer Engineer - Polytechnic School of A.U.TH.
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#4

Re: Medium & High Voltage existence check device

11/02/2009 3:23 PM

Dear Haris Kal,

Guest provided a good link, but you will need one of these of the appropriate length, approved gloves in some instances, and an experienced operator, since these voltages carry a terrible penalty for mistakes as you have acknowledged in your question.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Anonymous Poster
#5

Re: Detecting Medium or High Voltage Inside an Electrical Panel

11/02/2009 11:26 PM

Hi Mr. Kalothetos,

If your electrical panel is supplied by a three phase system you could use a protection/fault detection relay, as presented in

http://www.cooperpower.com/Library/pdf/03046.pdf

or

http://www.macromatic.com/products/phase-monitor-relays.html

The idea is to test the insulation of each phase and of the null (if there is an insulated null). Dangerous tensions can appear only if the insulations are weakened.

Marius Balas (marius.balas@ieee.org)

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#6

Re: Detecting Medium or High Voltage Inside an Electrical Panel

11/03/2009 12:54 AM

The most important issue BEFORE getting into ANY panel is LOCK OUT-TAG OUT.

Any effort to work in a "hot" (especially over 1000V) panel is bordering on suicidal.

If there is NO other way, isolate ALL conductors and devices not involved with cloth made of neoprene-encapsulated fiberglass hung over the panel from the top and clamped to the isolating cover using fiberglass spring clamps (with fiberglass leaf springs formed to fit internally) so only device being serviced is exposed.

Then- test all exposed contacts to be sure that cables are de-energized. Also, in addition to wearing "rated gloves", be sure that you are in shoes with di-electric soles and/or stand on DRY multi-layer rubber sheeting. Also- BE SURE THAT THERE IS AT LEAST 60 INCHES (1.5 METERS) OF CLEAR AREA BEHIND YOU (NOT in front of the panel) to eliminate the risk of you becoming a conductor between a hot wire and a ground point) and to allow for falling back to extricate yourself in case of contact with a hot line.

Better planning eliminates the need for luck.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#8
In reply to #6

Re: Detecting Medium or High Voltage Inside an Electrical Panel

11/03/2009 11:58 AM

energygod,

A well written and excellent post. I predict you will be a good asset to this site and a valuable resource for the many good folks who need to know what experience has provided us.

Regards and welcome, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply Off Topic (Score 5)
Participant

Join Date: Apr 2008
Location: Thessaloniki - Greece
Posts: 4
#7

Re: Detecting Medium or High Voltage Inside an Electrical Panel

11/03/2009 4:47 AM

Thank you all for your answers! They were all very helpful to find what i need and also expand my knowlegde. Keep up the good work! Best regards to everybody. Charalampos

__________________
Charalampos K.Kalothetos - Dipl. Electrical Engineer & Computer Engineer - Polytechnic School of A.U.TH.