Anonymous Poster

LSFCable

11/05/2009 5:25 AM

LSF(Low Smoke & Fumes) cables are fully fire resistance cable or partially fire resistance cable? pls reply me we require flame retardant cable but vendor supplied the cable LSF outer sheeth, is it ok? pls reply me....i will be greatfull to you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: LSFCable

11/05/2009 6:19 AM

The abbreviation LSF merely indicates that, in the case of flame impingement on the cable, they produce Low Smoke and Fume levels.

As to the suitability of LSF cables, it depends entirely upon the purpose of the installation, which isn't stated in the original post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#2
In reply to #1

Re: LSFCable..plz help

11/05/2009 7:22 AM

i am mentioning below the our specifications

OUR ENGINEERING SPECIFICATION

type : CU/XLPE/SWA/flame retardant outer sheath

service : for motor power and utilities

Installation : on cable trays

flame property : flame retardant outer sheath

nominal voltage rating : 600/1000V

operating temperature : 90 deg centigrate

temperature during fault condition: 250 deg cent

sizes : 4cx240sqmm, 4cx35sqmm,4cx300sqmm,4cx16sqmm,3cx2.5sqmm

ambient temp : - 10 deg cent to +50 deg cent

tests reports : high voltage test, insulation resistance test , partial discharge test

Received cable from vendor is

above sizes , CU/XLPE/SWA/LSF 600/1000V

PLZ advise me wheather the received cable satisfy minimumflame proof requirement or not .

vendor denies to give any test reports including flame proof certificate.

waiting for reply. plz help me.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: LSFCable..plz help

11/05/2009 8:13 AM

<...the received cable satisfy minimumflame proof requirement or not...>

The assessment needs to be carried out by the recipient on the basis of the user's requirements, and not on the basis of source-protected replies to a global engineering forum!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#6
In reply to #2

Re: LSFCable..plz help

11/05/2009 9:59 AM

Let us take another look at this. Your specification says:

type : CU/XLPE/SWA/flame retardant outer sheath

Your contractor supplied:

Received cable from vendor is above sizes , CU/XLPE/SWA/LSF 600/1000V

You didn't get what you ordered, now did you.

Sounds to me like payment withheld will get you the proper material, or the documentation that material supplied is, in fact, within your specifications.

Why are you bothering to do your vendors job? If he wants a check, he must perform.

__________________
Semper Ubi Sub Ubi
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#9
In reply to #6

Re: LSFCable..plz help

11/05/2009 4:27 PM

Something occurs to me that might interfere with this...

One of the great forces is the Lever. Money held back gives YOU a lot of LEVERAGE in this case.

Now, the bad thought... have you already paid this guy? If yes, your leverage has just been diminished a whole bunch! If not, then you will get what you want if you apply this force. Guaranteed!

__________________
Semper Ubi Sub Ubi
Reply
Member

Join Date: Oct 2009
Location: Hornell, NY
Posts: 6
#8
In reply to #2

Re: LSFCable..plz help

11/05/2009 1:53 PM

Hello,

It is up to your purchaser when requesting a quote for an item, that the quote received, matches the requirements of the request. If this was done correctly and the order placed with a po, I have found it common practice in the terms of a purchase order to be listed "Certificate of Compliance Required".

If the vendor refuses or is unable to provide this, do not use the product!! Weather it appears to be the correct item or not. If there is ever a safety issue, say a transit car derailment, investigating authorities may very well come knocking on your door to provide proof of compliance.

You have every right to return the product and demand credit to the invoice. Of course this does not satisfy your immediate need, but it will keep your $$s to purchase the correct product and cover your ..... self :)

Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#3

Re: LSFCable

11/05/2009 7:23 AM

You need to find out from the cable data sheet or from the cable manufacturer whether the supplied cable is flame reistant or flame retardant cable. LSF doesnot mean that a cable if FR or fire resistant type.

__________________
Atlas Shrugged - JGD
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: LSFCable

11/05/2009 8:07 AM

<...minimumflame proof...>

The term "flameproof" usually means equipment and circuits designed to British Standard 60079 EEx d for use in potentially explosive atmospheres.

There is no requirement to use LSF cable for BS 60079 EEx d applications. Steel Wire Armour would be good idea, though.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #4

Re: LSFCable

11/05/2009 1:51 PM

Let's first see what Flame Retardant, Fire Resistant, LSZH and LSF actually mean.

Flame Retardant: Flame Retardance is the property of the substance, or a treatment applied to a material, whereby the propagation of a flame is markedly retarded. The insulation and jacket of flame retardant cable is made of the substance having flame redardance property so that the cable eliminates the fire propagation.

Fire Resistant: Cable can withstand and continue service in fire. A fire resistant cable is suitable for use in critical and emergency signal paths, such as, fire alarm systems or emergency lighting.

LSZH (or LSZH or LSHF): This type of cable uses insulation and sheathing materials that do not emit more than 0.05% Halogens (poisonous gases in particular hydrogen chloride), and have reduced smoke emission properties.

LSF: It produces low smoke but is not totally halogen free (can emit up to 22% hydrogen chloride). Basically it is an improved PVC cable. Obviously, it is less expensive than LSZH.

Halogens (Chlorine, Fluorine, Bromine and Iodine) are cheapest flame retardant material and are used with cable insulation (such as Chlorine in PVC) to increase its flame retardant property but cables made flame retardant by halogens produce smoke and toxic gases when it burns. Hence, the special insulation and sheathing materials are used in LSZH or LSF cables so that it is flame retardant as well as produces low smoke and low toxic gases. In most cases, the LSZH or LSF cables are flame retardant. However, they always may not be flame retardant. So, make sure with the cable manufacturer that the cable you received is flame retardant.

The following links may be further help:

http://www.fscables.com/pdf_info/LSHF.pdf

http://www.addison-tech.com/product/fiber-resistant.htm

http://www.drakact.com/dtc/files/Infoblatt_2005_01_Flammwidrigkeit_e.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Anonymous Poster
#10
In reply to #7

Re: LSFCable

11/07/2009 4:11 AM

thank you sir

i am grateful to you

thanks again.... I understood fully about the matter

Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#11

Re: LSFCable

11/08/2009 10:43 AM

Hello Guest,

The problem with posting as a guest is I do not know if all the 'Guests' on this thread are the same person or not? Get me?

Why do you not join. It costs nothing but five minute to enter your details, and the people are very helpful, especially when talking to other members! We are kind, good looking, sweet, extremely helpful and welcome any new skills a guest now member brings!.......... Let me rephrase that, ignore the "good looking and sweet" bit OK?

That being said, what exactly do you want to use this cable for?

There is a world of difference between a cable spec and its intended use.

This sounds obvious I know but, it would be easier to quote your use and ask for an appropriate cable, OK?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); babybear (1); Current Maarey (1); Doorman (2); kbirdnest (1); msamad (1); PWSlack (3)

Previous in Forum: sensors for electric and magnetic fields   Next in Forum: Motors and Capacitors

Advertisement