Anonymous Poster

Transformer Impedance

11/09/2009 12:07 AM

Hi All

I have a transformer 1200KVA 690/433V 5.09% impedance. I can calculate the short circuit impedance with these values. My question is can this be considered the overall impedance of the transformer. I am getting two values using two different methods. one is 0.0137 ohms and the other is 0.0073 ohms. Can some one please tally it up. I understand this a very basic calcs, but I need this value right so that I can calculate the total earth fault loop impedance and calculate the touch voltages.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Transformer Impedance

11/09/2009 12:11 AM

My question is can this be considered the overall impedance of the transformer. I am getting two values using two different methods. one is 0.0137 ohms and the other is 0.0073 ohms.

Answer to your question is NO.

How did you get the other values?

Reply
Anonymous Poster
#2
In reply to #1

Re: Transformer Impedance

11/09/2009 4:22 AM

Thanks mate

I will take you through the cals

----> sqr(V)/S = (sqr(433)/1200000) * 5.09/100 = 0.00795 ohms

----> 5.09/100 * 433 = 22V. FLA is 1600Amps

Therefore 22V/1600A = 0.01375

The second calculation is for the short circuit impedance and the first one is using the base values. Which one is correct??

Thanks again..

Reply
Anonymous Poster
#4
In reply to #2

Re: Transformer Impedance

11/09/2009 11:07 PM

hi guest,

can you explain the same method for 500KVA, 11/415V, 5%?

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Transformer Impedance

11/09/2009 9:29 PM

Use this example

Given:

Connection: D-Y (4160V/480V) Size = 300KVA Ipri = 79.92A Isec = 692.62A

PF = Cosq = 0.25 Sinq = Sin(Cos-1q) = 0.968

R = 1.7% = 0.017pu @ 300KVA base X = 4.96% = .0496pu @ 300KVA base

Using primary side:

Zact = Zpu x Zbase I = 79.92A Zbase= V2/Sbase = (4160)2 / 300KVA = 57.685W

Ract = (.017)( 57.685) = 0.98065W

Xact = (0.0496)(57.685) = 2.86119W

VD = IRCosq + IXSinq ÿFrom IEEE Red Book

VD = I[RCosq + XSinq]

VD = 79.92[(0.98065)( 0.25) + (2.86119)( 0.968)] = 240.85V

VD3q= VD x ÿ3 = 240.85V x ÿ3 = 417.16V

VD3q % = (417.16V / 4160V) x 100 = 10.03%

Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5

Re: Transformer Impedance

11/10/2009 5:16 AM

Connection: D-Y (4160V/480V) Size = 300KVA Ipri = 79.92A Isec = 692.62A

Is this correct or am I wrong ???

P = I x U x sqrt (3)

300 kVA = I x 4160 x 1.73 so Ipri becomes 41.7 Ampères ....

300 kVA = I x 480 x 1.73 so Isec becomes 361 Ampères ....

Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#7
In reply to #5

Re: Transformer Impedance

11/10/2009 12:43 PM

You are right.....even I doubted my calculating abilities...remaining part of reply by Wareagle also I couldn't get.

__________________
"Know something about everything and everything about something"
Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#9
In reply to #7

Re: Transformer Impedance

11/12/2009 7:08 AM

Nor did I understand the remaining part. .......

Perhaps Wareagle can explain it one more time ....

Or the one who rated this as a good answer ...

Reply
Member

Join Date: Oct 2009
Posts: 6
#6

Re: Transformer Impedance

11/10/2009 10:42 AM

you can consider it as overall impedance of the transformer .

before starting calculation , you have to assume base MVA, V, I, Impedance.

in your case

transformer impedance = 0.0509 * (base MVA / 1.2 MVA )

Reply
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#8

Re: Transformer Impedance

11/10/2009 2:02 PM

I can't quite make out what you are saying.

Could it be that the lower impedance is the series loss impedance (effectively the series resistance) and the higher one is the impedance at short circuit?

If so, the reason they are different is that the true short-circuit impedance must include the transformer's leakage inductance, whereas the loss impedance relates to the losses when the transformer is loaded with a largely resistive load - and the main effect of the leakage inductance is to change the phase of the output rather than the Voltage.

Reply
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#10

Re: Transformer Impedance

11/12/2009 7:59 AM

I looked up the standard definition of winding impedance: it is the effective series impedance (= leakage-inductance plus transformed winding resistances) of the transformer.
% winding impedance is the winding impedance as a percentage of the impedance needed to generate nominal loading.

There will be two values for this - one viewed from the supply side, the other viewed from the load. Which you want depends on the application.

Having said this, the numbers in the header-posting are both wrong. I wouldn't care to disinter how you got there, but the correct formula is:
Zwinding = Vnom2/VArating x (%impedance/100)

So the winding impedance viewed from the 690-Volt side is specified to be 0.02-Ohms, and the impedance viewed from the 433-Volt side is specified to be 0.008 Ohms.

(BTW, the full-load currents should be 1739 and 2771 Amp rms respectively, and it all comes out in the wash)

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#11

Re: Transformer Impedance

11/16/2009 6:38 PM

Sample Voltage Drop Calculation Across Transformer

XF2-001:

Given:

Connection: D-Y (4160V/480V) Size = 300KVA Ipri = 79.92A Isec = 692.62A

PF = Cosq = 0.25 Sinq = Sin(Cos-1q) = 0.968

R = 1.7% = 0.017pu @ 300KVA base X = 4.96% = .0496pu @ 300KVA base

Using primary side:

Zact = Zpu x Zbase I = 79.92A Zbase= V2/Sbase = (4160)2 / 300KVA = 57.685W

Ract = (.017)( 57.685) = 0.98065W

Xact = (0.0496)(57.685) = 2.86119W

VD = IRCosq + IXSinq From IEEE Red Book

VD = I[RCosq + XSinq]

VD = 79.92[(0.98065)( 0.25) + (2.86119)( 0.968)] = 240.85V

VD3q= VD x √3 = 240.85V x √3 = 417.16V

VD3q % = (417.16V / 4160V) x 100 = 10.03%

Using secondary side:

Zact = Zpu x Zbase I = 692.62A Zbase= V2/Sbase = (480)2 / 300KVA = 0.768W

Ract = (.017)( 0.768) = 0.013056W

Xact = (0.0496)( 0.768) = 0.0380928W

VD = I[RCosq + XSinq] = 692.62[(0.013056)( 0.25) + (0.0380928)( 0.968)] = 27.80 V

VD3q= VD x ÿ3 = 27.80 x ÿ3 = 48.15 V

VD3q % = (48.15V / 480V) X 100 = 10.03%

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#12

Re: Transformer Impedance

11/16/2009 6:49 PM

This is a correction to the first post

Sample Voltage Drop Calculation Across Transformer

XF2-001:

Given:

Connection: D-Y (4160V/480V) Size = 300KVA Ipri = 79.92A Isec = 692.62A

PF = Cosq = 0.25 Sinq = Sin(Cos-1q) = 0.968

R = 1.7% = 0.017pu @ 300KVA base X = 4.96% = .0496pu @ 300KVA base

Using primary side:

Zact = Zpu x Zbase I = 79.92A Zbase= V2/Sbase = (4160)2 / 300KVA = 57.685W

Ract = (.017)( 57.685) = 0.98065W

Xact = (0.0496)(57.685) = 2.86119W

VD = IRCosq + IXSinq

VD = I[RCosq + XSinq]

VD = 79.92[(0.98065)( 0.25) + (2.86119)( 0.968)] = 240.85V

VD3q= VD x ÿ3 = 240.85V x ÿ3 = 417.16V

VD3q % = (417.16V / 4160V) x 100 = 10.03%

Using secondary side:

Zact = Zpu x Zbase I = 692.62A Zbase= V2/Sbase = (480)2 / 300KVA = 0.768W

Ract = (.017)( 0.768) = 0.013056W

Xact = (0.0496)( 0.768) = 0.0380928W

VD = I[RCosq + XSinq] = 692.62[(0.013056)( 0.25) + (0.0380928)( 0.968)] = 27.80 V

VD3q= VD x √3 = 27.80 x √3 = 48.15 V

VD3q % = (48.15V / 480V) X 100 = 10.03%

Reply