11-kV Connection to 11-kV Grid

11/09/2009 8:47 AM

I am working on a project in which the 2 MVA(very small power)at 11kV is generated. We have to export the power to 11kV Grid. The mandatory & necessary protection will be provided & the intertripping will be done according.

My question is it mendatory to provide the galvanic seperation between the generator & grid i.e. to provide an export transformer between the 11kV Medium voltage panel & the 11kV Grid? or the direction connection to 11kV grid is possible.

__________________
Clean Energy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Dec 2008
Posts: 19
Good Answers: 1
#1

Re: 11-kV Connection to 11-kV Grid

11/09/2009 10:40 PM

I suggest you check the utility grid connect requirements. There also may be issues related to fault levels that need to be taken care of.

Amit.

Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#2

Re: 11-kV Connection to 11-kV Grid

11/10/2009 7:41 AM

It probably is not possible to hook directly to the grid. I have no idea what the Utility requirements are in Switzerland, but I am sure you will want some sort of synchronizer and protective relays to prevent backflow or other problems which will immediately take you off the grid for the grids protection as well as your own.

Also they would should want some sort of agreement signed as to how and when you can send power. Since it is still their responsibility to maintain the grid.

Register to Reply
Active Contributor

Join Date: Mar 2008
Location: Switzerland
Posts: 17
#3
In reply to #2

Re: 11-kV Connection to 11-kV Grid

11/10/2009 8:05 AM

Thanks for the reply,

The proper synchronisation is provided. Also the protection and the intertripping will be achieved between the network operator and the utility. Also the Generator circuit breaker is provided ( to tackle the fault current).

Definately the utility have to give the permission for this type of arrangement.

However, therotically,the galvonic separation is required or not?

__________________
Clean Energy
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4
In reply to #3

Re: 11-kV Connection to 11-kV Grid

11/10/2009 12:24 PM

Anant,

I have several generators connected directly to the 13.8KV distribution grid here. In theory and practice, it is readily achievable. My units vary in size from 1.2 MVA up to 28 MVA. Both the generators and the grid are owned by the utility (me), so getting permission is not a problem.

Assuming your generator is a grounded star connection, there is more risk to your equipment than to the utility. In a phase to ground fault, not only will your generation supply the fault, but there will be additional fault current coming through your neutral ground connection to feed the fault. All of my generators have large current-limiting reactors in the neutral leg between the wye and ground to prevent damage.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Active Contributor

Join Date: Mar 2008
Location: Switzerland
Posts: 17
#5
In reply to #4

Re: 11-kV Connection to 11-kV Grid

11/11/2009 4:12 AM

Thanks to pwr2thepeople for your response & valuable suggestion.

We had considered the Generator with isolated star point and an Neutral grounding Resistor is used of suitable rating ( for 10 sec).Also the resistor switched on to generator neutral point in case of isle mode.

__________________
Clean Energy
Register to Reply