Good morning,
I am having some problems with my pid loop in my automation direct plc that is controlling my condensor cooling.
I have an Automation Direct DL06-AR plc with an analog input/output card (i am at home and cannot remember what the model number is).
the plc controls the coolant to the coolant towers for an ammonia condensor system and the system is controlling a psi input set to 160 psi.
there are 3 coolant pumps that come on in a step configuration when the process value (pv) exceeds the setpoint with a 2 psi deadband.
after the 3 pumps, there are 2 fans that are controlled by vfd's that come on 1 at a time. these fans are the ones that are controlled by the pid loop in the plc. 0 to 60 hertz.
the problem that i am having is that the output of the pid loop is steadily climbing over a period of a few days, and apparently sticking at 60 hertz. so when the fans are called on, they ramp up to max output. they have also gone the other way and stuck at 0 hertz.
the setup of the pid loop is as follows: (setup was from chapter 8 of the do-06 users manual).
Config tab:
algorithm - position
sample rate - 0.05 sec
transfer mode - Bumpless 1
sp/pv & output format - common format
common data format - bipolar data format
- 12 bit data format
sp/pv tab:
nothing is set on this tab.
output tab:
upper limit - 4095
lower limit - 0
tuning tab: (these values have been adjusted to various levels. the ones listed are the latest values)
gain - 2
reset - 30 sec
rate - 0
all other values are default including the alarms and r/s tabs.
apparently, the bias value (which can be monitored and adjusted from the pid view pane in directsoft 5 software) is climbing and sticking at a value of 4095.
any help would be greatly appreciated. I am also new to plc's and apologize for any missing information, which i will gladly provide.
Thank you,
Ken Edwards
Engineering Student
Maintenance Man