LT and HT Switchgear - Why Both?

11/10/2009 10:08 PM

I have a very basic question...I visited a 3MW power plant recently and found their configuration to be: generator->LT circuit breakers->step up transformer to 33kv-> HT circuit breaker -> grid line.

What is the need for circuit breakers on both LT and HT side? I figured if there were any high load draws or voltage surge on grid, the HT breaker should take care of it all. Can anyony explain this?

RR

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Need for LT and HT switchgear, why both?

11/10/2009 10:35 PM

The reason for doth is due to the need for electrical discrimination. In the event of a transformer fault the LT circuit breaker protects the plant generator from damage (remember due to impedance the fault is likely to be feed primarily by the plant generator AND partly by the HV grid). Also in the event of a plant generator fault or wiring fault the LT circuit breaker protects the transformer.

Additionally the LT circuit breaker can be used as an isolation switch to allow safe working on the transformer when the plant generator is still running (obviously this will depend on the circuit configuration).

__________________
jack of all trades
Reply Good Answer (Score 2)
Anonymous Poster
#2

Re: LT and HT Switchgear - Why Both?

11/12/2009 3:27 AM

Those breakers are there for all around protection and operations; for the Generators, for the tranformer(s) and the Grid. Damaging electrical faults can occur in any of the components that make up this system; Generator> Transformer > Grid; in addition to the need to occasionally shut down and/or isolate the generators or the transformer from the grid for maintenance or rest. In addition, as part of the protection scheme there will be controls to properly synchronize each component, the breakers play an important role in that function.

Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#3

Re: LT and HT Switchgear - Why Both?

11/12/2009 5:09 AM

If the power plant is connected to a grid, then power could flow in either direction. The grid need to be protected from a transformer fault, hence the fuses on the HT.

Reply
Anonymous Poster
#4

Re: LT and HT Switchgear - Why Both?

11/12/2009 12:46 PM

Think about what the circuit breakers are protecting and you'll have your answer!

Reply
Anonymous Poster
#5

Re: LT and HT Switchgear - Why Both?

11/13/2009 8:37 AM

Note that the transformer is inbetween LT and HT side.It has primary(coil)winding LT and secondary(coil)winding HT.The primary side takes care of the LT circuitry and associated circuits while the secondary side takes care of the HT circuitry and other associated circuits.Just as you are aware of faults on the HT side and the need for its protection,so are faults on the LT side and the need for its protection using LT circuit breakers.Recall that when loads are switched,there is current flow from primary LT to the secondary HT or vice-versa through the Transformer(ie-Transformation principle).If fault occurs on primary side,it can damage devices,components and or equipment on the primary circuit,if there is no protective device on the LT side.Note also that the LT breaker has a different current trip setting from the HT current trip setting due to current and voltage differential values on both sides.Apart from the above reasons,the LT and HT breakers also provide isolation(Break in Contuinity) to enable work to be done by personnel on either side for safety of life and property.

Reply
Anonymous Poster
#6

Re: LT and HT Switchgear - Why Both?

11/14/2009 4:23 AM

Note that the Transformer is inbetween LT and HT side.It has primary(coil)winding LT and secondary(coil)winding HT.The primary side takes care of the LT circuitry and associated circuits while the secondary side takes care of the HT circuitry and other associated circuits.Just as you are aware of faults on the HT side and the need for its protection,so are faults on the LT side and the need for its protection using LT circuit breakers.Recall that when loads are switched,there is current flow from primary LT to secondary HT or vice-versa through the transformer(ie Transformation principle).If fault occurs on primary side,it can damage devices,components and equipment on the primary circuit if there is no protective device on the LT side.Note also that the LT breaker has different current trip setting from the HT breaker current trip setting due to current and voltage differential values on both sides.Apart from the above reasons,the LT and HT breakers also provide isolation(Break in Contuinity) to enable work to be done by personnel on either side for safety of life and property.

Patrick Whowha

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); Chankley (1); jack of all trades (1)

Previous in Forum: Number of of Earth pit per diameter size?   Next in Forum: Connection of Instrument Earthing & Electrical Earthing at the end
You might be interested in: Circuit Breakers, Load Centers, Circuit Tracers

Advertisement