Anonymous Poster

Connection of Instrument Earthing & Electrical Earthing at the end

11/10/2009 11:53 PM

Halo everybody

Is it feasible or technically correct to connect seperate Instrument Earthing & Electrical Earthing at the end of the seperate Earthing pits.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Connection of Instrument Earthing & Electrical Earthing at the end

11/11/2009 2:12 AM

http://www.eng-tips.com/viewthread.cfm?qid=142946&page=16

ALso Yogokawa and several other instrument companies recommend separate earth terminals (most likely to avoid the spike of the earth electrode voltage creeping back to instrument) - remember, though the earth resistance must be low (less than 1 ohm), still the high voltage may create a spike of quite a few voltage before the protection shuts it off.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Connection of Instrument Earthing & Electrical Earthing at the end

11/11/2009 9:54 AM
  • Feasible? Yes.
  • Desirable? Yes.
  • Technically correct? Yes.
  • A requirement? No.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#3

Re: Connection of Instrument Earthing & Electrical Earthing at the end

11/12/2009 3:25 AM

Thanx for your reply.

But I think I felt a little bit short to ask the right thing.

I'ld like to ask is it right or correct to combine both seperate Instrument Earth & Electrical Earth in any of the earth pits. (Both shorted either in Instrument Earth or Electrical Earth).

Let me explain precisely

1) Seperate Instrument Earth

2) Seperate Electrical Earth

3) Both Earthings are combined or shorted with each other in the Earth pits with a piece of cable grounded in both Instrument & Electrical Earths.

Reply
Anonymous Poster
#4
In reply to #3

Re: Connection of Instrument Earthing & Electrical Earthing at the end

11/12/2009 3:42 AM

This really may not be a problem (this is the previous guest- that has said no and then provided the link)

The point is that we do not want the spike to travel back, whose magnitude depends on the fault level in the power line.

However since your connection between the electrodes is within pit, this problem is not likely to occur.

However in case of sensitive instruments, just contact the manufacturer, since we don't want the guarantee to be nullified due to these minor things.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #3

Re: Connection of Instrument Earthing & Electrical Earthing at the end

11/12/2009 9:08 AM

In fact, it must be what you have said. (i.e.) Seperate Instrument Earth, Seperate Plant Earth and LINK both at the earth level. This is what is recommended strongly in IEEE 1100 too.

Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#6

Re: Connection of Instrument Earthing & Electrical Earthing at the end

11/13/2009 9:10 AM

Can be done..but take care that there is no more than one panel earthing leads going to the grid causing a loop in case of big spike it can pass a current through the panel thru those earth points connected at diffenerent points having different voltage levels on fault.

__________________
"Know something about everything and everything about something"
Reply
Participant

Join Date: Apr 2010
Posts: 1
#7
In reply to #6

Re: Connection of Instrument Earthing & Electrical Earthing at the end

04/23/2010 12:57 PM
Reply Off Topic (Score 5)
Reply to Forum Thread 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); electricalexpert65 (1); giri (1); PWSlack (1); ReyVax (1)